    Long swa run to campsite 2c or 3c???......,

    humm 0.35 is poor & high! I get 70mm by the skin of my teeth on cablecalc but 95mm on other software so I would be looking at 95mm. I would also be looking at trying to get that ze down. You did say BS88 63a with 60a load and 180m
  2. S

    Long swa run to campsite 2c or 3c???......,

    Have you got a site ze reading? as this could be the difference between 70mm and 95mm as I dont think you will get disconnection times for 50mm
  3. S

    I'm told this is against regulations?

    Well the risks are only going to get worse with more chargers installed.
  4. S

    I'm told this is against regulations?

    It says that if you can't meet the requirements you can still use TN system if its a dwelling. The code of practice goes on to say that there are way to help reduce the touch voltage as getting the required low Ra is unlikely. I'm not saying it does not happen but how many open circuit PEN...
  5. S

    I'm told this is against regulations?

    page 26 its also in your bs7671 page 279 Why make it all TT when you can just connect the rod to the MET like i think they are asking in the 18th
  6. S

    I'm told this is against regulations?

    I think you need to do some reading too :)
  7. S

    16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

    What manufacture is your charging point? as all the ones I have read ask for a 20amp MCB.
  8. S

    I'm told this is against regulations?

    As I said you need to do some reading. It’s all made very clear in the IET code of practice for electric vehicle charging equipment installation.
  9. S

    I'm told this is against regulations?

    Are you sure? I think you need to do some reading up :)
  10. S

    16 amp socket help please

    I like the T+E feeding it, look a top job !
  11. S

    16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

    What does he need to clamp it for? He has designed it correctly and no parts are in danger . No code and I don’t see how you can code it.
  12. S

    16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

    lol, I was expecting to see lots of pic's online of earth rod explosions and like but nothing yet (that I have seen) but I feel its coming. :)
  13. S

    16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

    20 amp should be fine supplying your 16amp socket as you say its covered in OSG part H3. Out of interest have you hit mainly drains installing your earth rods for your EV chargers ?
  14. S

    Best type of lighting in stables

    The Department for Environment, Food and Rural Affairs (defra) tell you in there "Code of Practice for the Welfare of Horses, Ponies, Donkeys and their Hybrids" that your electrical installation should be installed/maintained and tested to current BS7671. Part P has nothing to do with what you...
  15. S

    Why are wall chasers so expensive

    It's because they don't sell many in comparison to normal grinders, it's a bit more specialized.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock