Could anyone shed some light on what might be going on here, before I cut a trap in the laminate to find out. I have a dead socket on the end of a 2.5mm cable of unknown origin. L-E L-N N-E all 0 volts. Insulation resistance between the ends all 1000M Ohm. No continuity any conductor back...
Hi guys, if 16 RCBO neutrals are tie wrapped together for neatness, are there any thermal considerations such as grouping factors to be taken into account?
A kitchen fitter did something which took out the breaker in the plantroom but not any mcbs on the consumer unit in the apartment. I insulation resistance tested the submain and it was fine.
Hi guys, why might a fault on a final circuit in an apartment trip the dp c63 submain circuit breaker in the plantroom but not any mcbs on the consumer unit in the apartment?
I have no problem with being taught how to suck eggs. If I need to be told, I'm grateful that someone is willing to tell me.
I am getting a little deja vu on your point about insurance and legal issues. Last year, I was warned off making a basic smoke vent controller by a fire officer after I...
Thanks for the reply. You have given me much needed information.
The float switch contraptions have been custom made and are fitted into the RC floors of the plant rooms of each level of an apartment block. ( The horse bolted after an almighty flood ). They have two flying leads for the switch...
Hi, the application is of a flood sensing float switch which would in turn operate a 24v motorised valve cut off valve for the mains water.
The level relay you mentioning sounds promising. Do you think it would work for this application?
Hi guys, I want to switch a 24 v load on using just the continuity of NO voltage free loop. Does anyone know of a relay or device or method that I could use to do this?
thanks
thanks for the reply. i don't know why C types specifically were used. there is no documentation available, however the circuits are for general use socket outlets, no fixed loads, motors or IT suites.
i believe the Zs values are accurate and are the result of long circuits rather than...
Hi all, i'm doing an eicr on a school and am live testing ZS for ring final circuits. The supply is TNCS. i have two results and three questions if i may. i'm getting
c32 rcbo ZS 0.64 ohms. ( Max ZS allowed 0.55 ohms ) Should this be coded a C3 because although ZS fail, the rcd will catch...
Yes, the amount of time I was allocated for the job certainly influenced my decision. To clarify, it was on to the next circuit that I moved after the FI.
Doing an eicr on a landlord board, in a small 1940s block of bedsits, found a type 2, 30amp socket ring breaker with 5 x 2.5mm cables in it. I assume that 2 of the wires came from an empty adjacent 30 amp heater ring breaker that had been damaged (screwdriver busbar metal board bang) and the 5th...
PROUD TO BE A MENTOR IN THE TRAINEE SECTION.
there are some mentors a trainee can do without. you know what happens when you ridicule someone for asking a question? they stop asking questions.
not me though. i'm too old to give a ****.
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.