    Which is better BS1361 or BS88?

    Was wondering why was BS1361 replaced by BS88 even though BS1361 tends to have a larger breaking capacity according to the on-site guide if I'm reading it right, however, I maybe wrong. For example BS1361 breaking capacity can be 16.5kA to 33kA depending on what type you get, where BS88 is 16kA...
  2. K

    calculating csa of earthing conductor with BS1361 fuse

    Maybe I'm overlooking the obvious but how would you calculate the min. csa of an earthing conductor of say a tn-s system when there is no time/current graph for a 1361 fuse in the BGB? Do you just obtain If from Uo/Ze and then use this in the adiabetic equation. Ta
  3. E

    BS1361 fuse type 2

    Can you get this fuse with a 12kA short circuit capacity. I've got an EIC saying so. I personally thought they were between 16.5 and 33kA?