K

knasher

Maybe I'm overlooking the obvious but how would you calculate the min. csa of an earthing conductor of say a tn-s system when there is no time/current graph for a 1361 fuse in the BGB? Do you just obtain If from Uo/Ze and then use this in the adiabetic equation. Ta
 
OP
D

Deleted member 26818

Look in a copy of the BRB, or obtain the information from the fuse manufacturer.
You would not be able to conduct the adiabatic equation without this information, as you require a value for 't'.
 
OP
K

knasher

Thanks Spinlondon, ive still got BRB somewhere, so will dig it out.
 
OP
K

knasher

As a matter of interest, what is the logic behind IET not bothering to do time/current graphs for certain fuse types?
 

ruston

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
5,539
Location
Northumberland
From the BGB -1361 spec for cartridge fuses for ac in domestic or similar premises replace by BS 88-3: and withdrawn 1/3/2010.
 
Last edited:
OP
K

knasher

Hi rushton, are you saying BS88-3 is now the replacement for the 1361 fuse? or that BS88-3 replaced the BS1361 fuse but now not deemed as a suitable replacement? Just trying to get this clear in my head please
 

chocca

Active EF Member
Messages
34
Location
Sunny Sunderland
So, to satisfy an old man's confusion, if the installation has a BS1361 fuse and it's now been turned into a BS88 type 3 by the magic of the BGB, do you use the info for BS88 fuses in the tables?
 

ruston

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
5,539
Location
Northumberland
Yes as understand it the spec for BS 1361 has been removed and replaced by BS88 -3: 2010 . It's on page 277 of the green book. and the book will only list the current standards. Appendix 1 on the top of the page gives the criteria.
 

ruston

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
5,539
Location
Northumberland
So, to satisfy an old man's confusion, if the installation has a BS1361 fuse and it's now been turned into a BS88 type 3 by the magic of the BGB, do you use the info for BS88 fuses in the tables?
I would still use the old specs its as clear as mud.
 
OP
D

Deleted member 26818

It's the same as with the old BS3871 MCBs.
Still in use, but the time current curves are no longer in BS7671.
 