Hi all,

After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth.

I believe it to be a TN-S as the main earth is attached to the back of the main incoming cable. In December, I got the CU replaced and isolator fitted and was advised by an electrician that cut-out replacements would alter the earthing system to TN-C-S or PME.

This morning, the DNO dug up the pavement (assuming they cut the cable) and reconnected after the replacement. However, the main earth was not touched at all. It is 4mm2 cable that goes behind the incoming cable is just stuck to the wall with no earth clamp.

The DNO measured the earth impedance using the live and neutral and quoted it was 0.3 with the maximum allowed is 0.8

I've attached photos. In the photos, you see two earths, the larger earth leads outside to the gas pipe, the smaller earth goes behind the incoming cable. Also, notice that the fuse carrier is not sealed.

Any advice much appreciated.
 

Attachments

  • IMG_20220815_151129.jpg
    IMG_20220815_151129.jpg
    230.2 KB · Views: 311
  • IMG_20220815_160421.jpg
    IMG_20220815_160421.jpg
    202.4 KB · Views: 181
  • IMG_20220815_151129.jpg
    IMG_20220815_151129.jpg
    230.2 KB · Views: 169
Last edited by a moderator:
I believe it to be a TN-S as the main earth is attached to the back of the main incoming cable.
Correct
In December, I got the CU replaced and isolator fitted and was advised by an electrician that cut-out replacements would alter the earthing system to TN-C-S or PME.
That would have been a fair guess, but it was a wrong guess as things turned out. No big deal.
This morning, the DNO dug up the pavement (assuming they cut the cable) and reconnected after the replacement. However, the main earth was not touched at all. It is 4mm2 cable that goes behind the incoming cable is just stuck to the wall with no earth clamp.
I think it is actually brazed to the lead cable. Rather difficult to say from photo.
The DNO measured the earth impedance using the live and neutral and quoted it was 0.3 with the maximum allowed is 0.8
I'm assuming/hoping they also had the test device connected to the 4mm earth wire with it disconnected from the metal MET block.
If so that's a good result and proves a decent connection.

As far as I can see, whether it's a 60 or 80A fuse in the cut-out, the regs are satisfied (adiabatic equiation) with a 4mm earth.
Worst case (lower limit) fault current of 766A . The max prospective fault current will be higher as the neutral is bigger, lower impedance = higher current = faster trip time.

For 766A fault current, 60A disconnection time is 0.2s. 80 disconnection time is 0.7s.
I get between 3mm (so 4mm) for 60A and 4mm for 80A.
At this point I'm not concerned.

If you have concerns it's a quick job to have a sparks verify the Ze (earth impendence).
 
  • Like
Reactions: MKhan7249
Correct

That would have been a fair guess, but it was a wrong guess as things turned out. No big deal.

I think it is actually brazed to the lead cable. Rather difficult to say from photo.

I'm assuming/hoping they also had the test device connected to the 4mm earth wire with it disconnected from the metal MET block.
If so that's a good result and proves a decent connection.

As far as I can see, whether it's a 60 or 80A fuse in the cut-out, the regs are satisfied (adiabatic equiation) with a 4mm earth.
Worst case (lower limit) fault current of 766A . The max prospective fault current will be higher as the neutral is bigger, lower impedance = higher current = faster trip time.

For 766A fault current, 60A disconnection time is 0.2s. 80 disconnection time is 0.7s.
I get between 3mm (so 4mm) for 60A and 4mm for 80A.
At this point I'm not concerned.

If you have concerns it's a quick job to have a sparks verify the Ze (earth impendence).
Would they still have maintained the TN-S supply after reconnecting?

By reconnecting I mean cutting and rejoining.
 
Last edited by a moderator:
Would they still have maintained the TN-S supply after reconnecting?
It looks like they did, and they told you an earth impedance and the max limit for TN-S, so the laws of probability say yes.
 
Cant do anything about the size of the main earth the DNO supply. We're only concerned about the consumer side not the supply side. If the supply company have tested their side and say that's the reading their getting then we have to go with that If your worried get it tested but its probably fine.
 
  • Like
Reactions: suffolkspark

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Main earth after cut-out replacement
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
MKhan7249,
Last reply from
default,
Replies
6
Views
3,385

Advert