Can an swa be buried outside prescribed zone? Not rcd protected!
Discuss Swa buried in the Electricians' Talk area at ElectriciansForums.net
Ooh, good answer.Swa is OK for outside zone with no RCD as long as other Regs don't require the protection for other reasons ...i.e. special locations etc
Not within special location, drilled through outside wall then chased in approx 500mm down wall to floorboards at a depth greater than 50mm. I wouldnt see a problem exept it was 50mm 4core 160A feeding hotel control panel..
Ooh, good answer.
I would add, "...assuming that the armour is earthed..."
You'd kinda hope, wouldn't you? But then... *I thin on that note it goes without saying
Not within special location, drilled through outside wall then chased in approx 500mm down wall to floorboards at a depth greater than 50mm. I wouldnt see a problem exept it was 50mm 4core 160A feeding hotel control panel..