Hi,
I'm doing a refurb of my house and as part of that all of the old plumbing and electrics have been replaced (by their respective tradesmen).
In the new world order the downstairs heating is run off a 9 port polypipe ufh heating manifold and a new system boiler and megaflo have been placed in the loft.
The boiler and the megaflo each have their own dedicated radial circuits (and FCU's) running back to the consumer unit.
The ufh manifold is in a utility room which has it's own ring circuit and a FCU to power the pump and wiring centre.
The consumer unit is a Hager one populated with rcbo's.
When the heating engineer came to install the 3 nests (to control separate zones on the ufh and the water) we ran into issues.
Running the nests to control the manifold, pump, actuators, and the wiring centre downstairs all seemed to work fine.
The loft has it's own wiring centre for the boiler and megaflo (S plan circuit). Which also appears to work fine independently.
When connecting the 2 systems together - that's when the issues started.
When the connection to either the heating or water was triggered (from the nest) the rcbo's for both the utility room ring and the boiler would trip.
Initially he thought the cable between the loft and utility room might be the cause, but that was eliminated.
Ultimately he was unable to diagnose what the issue was on the day and is coming back this week to fix it.
I noticed that a neutral cable on one of the double sockets on the utility room ring was loose - could this have contributed to the rcbo's tripping when a heating or hot water call was made to the boiler?
It's also been suggested that the wiring centre in the loft and the one for the ufh manifold downstairs need to be powered by the same connection otherwise they will keep on tripping - does anyone know if this is correct and the way the system should be wired?
Thanks for your help
Because the different systems are on different circuits, when they become interconnected, there will be an imbalance in the line and neutral that the RCBOs are picking up on resulting in the tripping.
The entire heating system should be run as a single circuit (that doesn't mean one long radial circuit necessarily, but all powered from the same protective device).
Thanks - very much appreciated.
The boiler is currently on a 16A rcbo.
Do you think I will need to get the sparky back to swap if for a 20A one if adding the ufh manifold onto the same radial?
Reply to 3 Nests, Boiler, Megaflo and UFH - wiring assistance in the Central Heating Systems area at ElectriciansForums.net
Hi all, I've noticed that my UFH pump is not always turning on as soon as the stat & valve calls for heat. This results in hot water passing...
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...