Hi all i was wondering if anybody could shed some light on this equation or part of it. I think i understand how to work out the equation its self but its this part i dont understand.

In order to apply the adiabatic equation we first need to calculate the value of I (fault current) using this equation - I=v/zs. I undersatand zs is the earth fault loop impedance but where does the zs figure come from in ordor for me to divide the volts by it. i understand how to do a zs test when cables are installed, but how do you come across the figure before you start running cables?

any examples or advice would be great,

Thanks Chris
 
If the circuit length is known then the equation Zs = (Ze+(R1+R2)) may be used to find If

Alternatively the I2T values for the protective device from the manufacturer may be used.
 
  • Like
Reactions: 2 people
the only way to determine Zs before installing cables is to know the cable length and resistivity. then you can calculate R1+R2 from table 9A osg, then add that to Ze (at design stage, you would get this by enquiry) that gives you Zs.
 
  • Like
Reactions: 2 people
On a design you have to use the equation of Zs = Ze + ( R1 + R2).

The R1 + R2 you have decided to use a 2.5mm /1.5mm singles for a radial circuit that is say 27 metres in length. So it would be

19.51 X 27 / 1000 = 0.53 ohms.

The trouble then with a design question is you need the Ze and in most cases this is not available from measurement and therefore you can only get it by inquiry. If you can't then you have to either A take a Ze from a next installation or use the guides, so for a TNC-s it would be 0.35 ohm

So now you will have Zs = 0.35 + 0.53 = 0.88 and there you have the Zs.
 
  • Like
Reactions: 2 people
fastest fingers Lenny..
 
If you have the use of a loop tester you can measure direct but watch yourself as its a live test and you will be working close to energised components. If you dont have access to a loop/pfc tester then by calculation (as above) Dont forget that some loop testers dont have what we call a low current facility so when doing a Zs on an RCD/RCBO protected circuit the RCD/RCBO wont stay in. This is also the case for robin type testers that featured a device called DLOC.....the device would give the RCD/RCBO a shot of DC which had the effect of "freezing" it so it would stay in during measurement.....but modern RCDs will detect it and wont stay in as a result....you can wire em out however or do a Ze +R1 R2 as above
 
and when using the calculated figures for design you should also use a Multiplying factor of 1.2 to take into account increase in resistance due to operating temp
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
adiabatic equation help!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
schoe,
Last reply from
GLENNSPARK,
Replies
10
Views
1,683

Advert