So would removing the 4.0mm2 T&E cable allow enough space to meet the 45% space requirement?

Also would you guy know what the regulation is called or the number?

I have a strong feeling what response I am going to get from the electrician when I mention this but I will try.
 
Short answer NO.
BS7671 Guidance note 3, page 28 2.6.3 Conduit Systems paragraph 3 Recommended quantity of cables for easy draw not exceeded during installation causing insulation damage; .......... Item should be inspected during the erection stage as the care and workmanship of the installer can be verified (522.8.1 and see On-Site Guide Appendix E)

My spoon has just worn out.
 
Last edited:
  • Like
Reactions: Master Mech
Short answer NO.
BS7671 Guidance note 3, page 28 2.6.3 Conduit Systems paragraph 3 Recommended quantity of cables for easy draw not exceeded during installation causing insulation damage; .......... Item should be inspected during the erection stage as the care and workmanship of the installer can be verified (522.8.1 and see On-Site Guide Appendix E)

My spoon has just worn out.

Many thanks for your time, help & patience.

Looks like I will be on the search for another electrician to put all these issues right which will be interesting as I am sure many will not want to put right another persons cock up.

Thanks again to everyone who has participated in this thread & for your input & advice.
 
  • Like
Reactions: DPG and westward10

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice On Rewire Of Lighting Circuit
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
122

Advert

Thread statistics

Created
Master Mech,
Last reply from
Master Mech,
Replies
122
Views
22,149

Advert