There are two methods of conducting an IR test where there is voltage sensitive equipment.
One is to link live conductors together and test to earth at 500V d.c.
The other is to test between individual conductors at 250V d.c.
Both tests will require the minimum resistance to be 1MΩ.
SELV and PELV circuits should be tested at 250V d.c. and the minimum resistance is 500Ω.
The way i read it is this.
You apply either 612.3.1 "Between live conductors and between live conductors and the protective earth"
or
612.3.3. "Live conductors connected together and protective earth"
Along with the above we also use 612.3.2. The test voltages are as in table 61 or if the equipment is vulnerable we may reduce to 250 v dc.
So if we have vulnerable equipment, we shall use 612.3.3 as our test method.
The voltage in table 61 states 500 V d.c though we may use 250v d.c.