Hi...

I think I know the answer to this question but just wanted to hear what others said..

I'm upgrading a CCU and as part of the job I have done an inspection of the current installation which was a diy job. I don't think the owner was qualified but they have done quite a professional job and 'generally' pay gogod note to regs and safety etc.

However, there is no earthing to gas and water. I queried this with the owner. All water pipes are plastic but they have connected the gas pipe using a 10mm cable to copper heating pipes which are then eventually bonded to the ring main so effectively going back to the CCU via a 1.5mm earth. These connections are inaccessible.

I know this should be a 10mm straight to th CCU and will advise as such but what code would this be. Presumably it is then up to the owner. Would this be put as an advisory note on the certificate.

Also the Ze was super low at 0.06. Its a TT system with the Earth also connected to a lead water pipe in the garden

Any thoughts
 
No earthing and bonding has to be up to scratch to issue the electrical installation certificate. The lead main cant be used as an electrode as I doubt its part of a private water supply. Water probably needs bonding as its lead incomer....the gas will almost certainly need bonding. If the customer isn't willing to accept this then walk away.
 
Last edited by a moderator:
  • Like
Reactions: Des 56
Hi bud,just out of interest,what inspections did you do,regarding the earthing,and how was the Ze measured?
 
  • Like
Reactions: Des 56
TT with Ze of 0.06 Ohms may be a measurement error ?
A typical good rod might give 100 Ohms (say), so this would need 1667 of them in parallel to get that result. Maybe measuring the bonding cable?
 
  • Like
Reactions: DPG and Des 56
Have you located the electrode.
 
I highly doubt your true ze is 0.06 ohms
 
I don't want to appear critical at all, but how can you be thinking of undertaking a CU change (or CCU as you call it), and leaving inadequate bonding with a "note on the certificate"? It's not "up to the owner" it is up to YOU to do it as per BS7671. How do you imagine a TT system would have a Ze of that value?
 
  • Like
Reactions: DPG
Hi...

I think I know the answer to this question but just wanted to hear what others said..

I'm upgrading a CCU and as part of the job I have done an inspection of the current installation which was a diy job. I don't think the owner was qualified but they have done quite a professional job and 'generally' pay gogod note to regs and safety etc.

However, there is no earthing to gas and water. I queried this with the owner. All water pipes are plastic but they have connected the gas pipe using a 10mm cable to copper heating pipes which are then eventually bonded to the ring main so effectively going back to the CCU via a 1.5mm earth. These connections are inaccessible.

I know this should be a 10mm straight to th CCU and will advise as such but what code would this be. Presumably it is then up to the owner. Would this be put as an advisory note on the certificate.

Also the Ze was super low at 0.06. Its a TT system with the Earth also connected to a lead water pipe in the garden

Any thoughts
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Bonding and earthing
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
Chrisknowlesuk,
Last reply from
Pete999,
Replies
13
Views
2,203

Advert