Hi guys, can anyone help with this please.
I've a new kitchen going in which will have an induction hob, main oven & a compact oven/ microwave.
Induction hob is 32Amp & 7350W
Main oven is 16Amp & 3450 W
Compact oven 16Amp & 3650 W
New wiring is going in so would it be ok to use 10mm cable on the hob with a 40 amp fuse and a 45 Amp switch. Also a 10mm cable on a different 40 Amp fuse with a 2 way outlet & 45 Amp swich for the two ovens.
Hope I've explained this correctly.
Any help would be appreciated thanks.
 
Bit of an Overkill!
2No 32A circuits would be fine.
As for cable size, depends on route/length/volt drop, derating due to insulation etc.
 
  • Like
Reactions: Psycho61
diversity would normally let you use a 32A/6.0mm circuit, so if you use a 10.0mm on a 45A. you'll be fine, even if some itchy-poo on the cable route.
 
  • Like
Reactions: Psycho61
diversity would normally let you use a 32A/6.0mm circuit, so if you use a 10.0mm on a 45A. you'll be fine, even if some itchy-poo on the cable route.
I have taken out an old 10mm cable which was linked to a 40A fuse.
Just thought as all the kitchen cables will be renewed the 10mm would be more than adequate but don't want to go over the top as 10mm cable is not cheap.
Yes I'm a yorkshireman lol
 
As DefyG. But I’ve done exactly the same .,10mm to island unit with induction job and same for two ovens...but I do like to over engineer. ??
 
  • Like
Reactions: Psycho61
As DefyG. But I’ve done exactly the same .,10mm to island unit with induction job and same for two ovens...but I do like to over engineer. ??
 
I have taken out an old 10mm cable which was linked to a 40A fuse.
Just thought as all the kitchen cables will be renewed the 10mm would be more than adequate but don't want to go over the top as 10mm cable is not cheap.
Yes I'm a yorkshireman lol
why take it out when you could have re-used it?
 
Without knowing more about routes, de-rates and all that kinda stuff, sounds like 2 x 4mm radials would be fine (and a lot easier to work with).
 
why take it out when you could have re-used it?
It was damaged & not long enough because oven & hob ate in a different place. If you had seen the rest of the wiring, well let's just say it looked like a crow's nest. Who buries live cables in the wall covered in plaster, they did in this house?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Cable size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Psycho61,
Last reply from
Mike Johnson,
Replies
10
Views
2,454

Advert