D

djwhite

Hi, is there any one who can advise me if I can have a USA light fitting(110V) fitted in the UK and just use a UK light bulb that fits the bulb fitting or would the whole thing need rewiring? Appreciate advice
 
Hi, is there any one who can advise me if I can have a USA light fitting(110V) fitted in the UK and just use a UK light bulb that fits the bulb fitting or would the whole thing need rewiring? Appreciate advice

Depends if it is a straight forward light fitting without any lamp control gear or not!! If it has anything more than a lamp holder, then no you won't be able to use it without modification....
 
would need a bit of new wire inside.....maybe even a new lamp holder if it was a cheap one...

why do you want to use a USA fitting here, is it something fancy?
 
Depends if it is a straight forward light fitting without any lamp control gear or not!! If it has anything more than a lamp holder, then no you won't be able to use it without modification....

Thanks, this is a standard wired light fitting it has no lamp control gear.
 
Hi, I would not say this is a cheap one, I paid around $500. It is not really fancy, just quite large which is what I needed. We have a very high ceiling in a new room we built and I wanted a large light fitting. The US market caters for larger size rooms Vs what you can buy here in the same price range. It has standard type wiring and no control gear to the lamp, just standard screw bulb fitting. I have check a buld here and the standard ES bulb fits it.
 
Hi, I would not say this is a cheap one, I paid around $500. It is not really fancy, just quite large which is what I needed. We have a very high ceiling in a new room we built and I wanted a large light fitting. The US market caters for larger size rooms Vs what you can buy here in the same price range. It has standard type wiring and no control gear to the lamp, just standard screw bulb fitting. I have check a buld here and the standard ES bulb fits it.

I wouldn't have a problem using this light fitting in the UK. The internal wiring size and it's insulation voltage rating will be fine too....

The Edison Screw lamps are a standard size pretty much worldwide...
 
I'm on the understanding that there's only a slight difference in the European and US ES holders, about 1mm. To be 100% I would change the holders for European ones as that little bit of play could cause overheating. If it's single phase wiring I can't see there being many problems but I would be confirming the cable type and rating to be on the safe side.
 
I'm on the understanding that there's only a slight difference in the European and US ES holders, about 1mm. To be 100% I would change the holders for European ones as that little bit of play could cause overheating. If it's single phase wiring I can't see there being many problems but I would be confirming the cable type and rating to be on the safe side.

If there is a difference i've never noticed it before. On most of the projects i've been on, our ES light fittings and lamps come from several different countries, can't say i noticed any noticeable play from one fitting to another with whatever lamp was used. Not saying your wrong, just that i haven't seen any difference between Yank and European ES lamp holders and lamps... American Wire voltage ratings on LV have an absolute min of 300V, but more often than not will be higher. It will also be 90/120C rated in such a light fitting too...
 
No BsEn number then it shouldn't be used really, my field officer drummed it into me to check for them on PIRs. Could easily be a code 4 that
 
No BsEn number then it shouldn't be used really, my field officer drummed it into me to check for them on PIRs. Could easily be a code 4 that

I would have thought CE marking more appropriate than BSEN, would you code a TUV marked fitting if it did not also have BSEN markings
 
No BsEn number then it shouldn't be used really, my field officer drummed it into me to check for them on PIRs. Could easily be a code 4 that

BSEN numbers are european so your not going to find it on a fitting from the USA , just to point out there is no code 4 on a EICR (PIR) any more ,sorry its sunday and im being picky lol
 
No BsEn number then it shouldn't be used really, my field officer drummed it into me to check for them on PIRs. Could easily be a code 4 that

BS7671 [511.2] says "Where equipment to be used is not covered by a British or Harmonized Standard, ... the designer or other person responsible for specifying the installation shall confirm that the equipment provides at least the same degree of safety as that afforded by compliance with the Regulations."

I was taught that this does allow you to use things like one-off lighting fixtures etc, provided you verified it was safe before installing it.
 
  • Like
Reactions: 2 people
p11jor;610191[B said:
]No BsEn number then it shouldn't be used really, [/B]my field officer drummed it into me to check for them on PIRs. Could easily be a code 4 that

Come on now, ...Get real, this is a private person purchasing a light fitting from a standards originated country for his personal use!! It'll probably have a UR logo on it, or some other Yank certification.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can I use USA light fittings in the UK
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
djwhite,
Last reply from
Engineer54,
Replies
24
Views
31,667

Advert