Discuss Commercial Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
RmBo_0
Hi,
Went to move a few sockets yesterday in a fairly large commercial building. Before I started I thought I'd do a quick Zs test. Result was >2000ohm, so I asked if I could isolate the DB so I could test Ze/Zdb and R1+R2 but was refused. So I thought I'd try get a Zs from some other final circuits on other DB's but was getting same result at this point I was convinced it must be my tester. So I informed the management that I thought that there might be a fault on the supply earth but I needed to confirm it wasn't my tester even though I only had it calibrated last week. Went to a little unit I do some work for just to see if my tester was giving me a result and it was fine. Went back and told them they need to get the supplier out as soon as possible to check the earth and the reply was yeah leave it with us. Called back today to see whats happening and they hadn't even got in touch with the suppliers yet. Didn't look like they was that bothered either.
Where do I stand with this? I refused to do the work till it had been sorted. Should I send the company an e-mail just to say I've informed management about not having an earth fault path and need to get in touch with their supplier.
a strongly worded email with a read request and a recorded delivery letter ( keep a copy). that puts you in the clear if the ---- hits the fan.
Yeah that's what I thought. Even though I didn't commence with the work I still feel responsible because I found the fault.
They own the building. I have explained to them but all I got was we'll get it sorted. Going back tomorrow and getting it resolved one way or another.
It's really down to the owners or outfit responsible for the premises to notify DNO,unless they ok you to do this.Do as previous post re;email and written notification,have observed this situation before where tester bypasses building owners giving details of works supervisor,they ring him,(if they bother),he says it's sorted and no visit.You've done your bit,cover ---,move on...good work pressing on and checking your results,sometimes you can sit down with the lemmings for hours and they STILL head for the cliff...
I'll stick one of these on their window.
I ended up hand delivering a letter to the manager and asked him to sign it to say he'd read it and gave them a copy. Dare say they probably won't have me back.
Reply to Commercial Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...