If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Originally a Sp DB,now 3pDb 400v.
The plans have not been altered to suit,so circuits are the same.
Would you worry about the rings are on different phases & close to each other.
 
If its doesn't comply with the regs!
 
  • Like
Reactions: DPG
Would you worry about the rings are on different phases & close to each other.
Yes I would worry. Irrespective of whether a single or upgraded to a three phase supply, the installation should still comply with the regs!
 
  • Disagree
Reactions: Tes369 and DPG
Socket outlets simultaneously accessible when on different phases?
When the OP says different rings, I'm assuming he is referring to the socket outlets.
If he is referring to the actual cabling then maybe no problem.
 
Personally I would of made the rings all on the same phase,but I didn’t connect DB.
Or even asked for revised drawings,but once again you get hassle of other sparkies who know better....??
 
Socket outlets simultaneously accessible when on different phases?
When the OP says different rings, I'm assuming he is referring to the socket outlets.
If he is referring to the actual cabling then maybe no problem.
Regulation number?
 
Lighting used to be spread across phases to lessen the stroboscopic effect, as long as the sockets are marked up then there should be no issue
 
  • Agree
Reactions: 123
Socket outlets simultaneously accessible when on different phases?
When the OP says different rings, I'm assuming he is referring to the socket outlets.
If he is referring to the actual cabling then maybe no problem.
I also am interested in why you think this does not comply to regulations, there is no issue at all here and if I recall there was once a regulation which called for them to be marked with a caution label if within arms reach of each other but I don't believe that exists anymore.
So in your own opinion what are the dangers or concerns here?
 
  • Like
Reactions: DPG
Don't know off hand but will check regs when back in the office.
May even be excluded in the 18th now but regardless of that, always seemed 'good practice' to prevent simultaneous contact!
 
I recall there was once a regulation which called for them to be marked with a caution label if within arms reach of each other

Maybe this is the reg that remember !!! Perhaps not valid anymore with the 18th??
 
Maybe this is the reg that remember !!! Perhaps not valid anymore with the 18th??
I think it dates back to the 16th and was lost when they redefined the regulation about marking switch points and outlets in excess of 230v, this was later altered to 230v to Earth which thus covered standard 3ph 400v and meant no labelling was required.
The original regulation is still in use but the goal posts where moved in its effect.
 
I think it dates back to the 16th and was lost when they redefined the regulation

16th - Was it really? Some things stick in the back of your mind regardless of changes in the regs!
 
16th - Was it really? Some things stick in the back of your mind regardless of changes in the regs!
It was the 16th. However the intent was always voltage to Earth and not between phases so this was clarified.
 
  • Like
  • Agree
  • Informative
Reactions: DPG, Andy78 and 123
always seemed 'good practice' to prevent simultaneous contact!
Why would you be simultaneously contacting live parts?!
 
Why would you be simultaneously contacting live parts?!

You wouldn't 'Would You'?
Thought the idea was to try to prevent simultaneous contact!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Different phases in offices
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
cliffed,
Last reply from
MJPD29,
Replies
33
Views
7,619

Advert