Is it just me who doesn't really see theis as an issue, as long as they fit right?
The issue with fitting MCBs/RCBOs/RCDs from one or multiple manufactures in a different manufacturers enclosure is that the original manufacturers BS EN 60439-3:1991+C:2009 type testing becomes null and void, because they quite reasonably only type test with their own protective devices. It then becomes the electrician's responsibility to ensure the assembly meets the requirements of the standard, this certification can only be gained via destructive type testing at a proof laboratory. I believe there is still a High Court case pending on this very issue, where an electrical contractor is being sued for £M in damages by insurance companies and others, resulting from an electrical fire at the distribution board.
The issue with fitting MCBs/RCBOs/RCDs from one or multiple manufactures in a different manufacturers enclosure is that the original manufacturers BS EN 60439-3:1991+C:2009 type testing becomes null and void, because they quite reasonably only type test with their own protective devices. It then becomes the electrician's responsibility to ensure the assembly meets the requirements of the standard, this certification can only be gained via destructive type testing at a proof laboratory. I believe there is still a High Court case pending on this very issue, where an electrical contractor is being sued for £M in damages by insurance companies and others, resulting from an electrical fire at the distribution board.
This question was asked at Elex today and answered by a panel consisting of 1 x Elecsa, 1 x Napit and 1 x NICEIC gentlemen. They said that the responsibility to ensure compatibility was down to you to check with the manufacturers - and if they won't say "yes ok" then its down to you!!!!!!!!!
I'd like to see the proof the so-called expert witness puts up to prove an MCB that was manufactured in the same factory, on the same machine but with a different company logo printed on it, was the cause of whatever damage this insurance company claims.
In essence, this makes the whole business of type testing MCB'S as a nonsense!! Different if someone has shoehorned in a totally different MCB casing with a bus bar connection that don't line-up etc!! ...lol!!!
As I understand it the case won't hinge on that issue at all. The prosecution will only have to establish that type testing for the assembly wasn't obtained by the electrical contractor who did the work and they will have established reasonable doubt and lack of credibility of the contractor and their staff.
OK, then...now begs the question when is a DB not a DB? If I take an adaptable box with a DIN rail, and a nice cover (Lewden do some lovely ones)....insert 4 x MK MCB's, an RCD and an Isolator switch.....absolutely nothing wrong with that as far as I can see..... do I have an MK board or a Rockingit board???
FFS - it's a plastic moulding that's being argued over, surely??
In your example the breakers are all the same make. I think it is mixing the makes that causes the contention? Hager instructions say that only products from their catalogue should be installed.