Hi everyone. Found you guys through Google and can see this a good site. So I'm hoping some of you can answer some questions for me regarding the subject.

So our garage has no power provision but I want to install some LED lighting so I can work on our motorcycles without being troubled by the current deluge of rain hitting the UK.

I'm not an electrician but I've wired a few circuits in the house and replaced fittings, sockets etc. Nothing major.

An electrician told me roughly what would be involved to carry out this work, but I still have some questions.

Would I need to get the work certified upon completion if I were to do it myself?

There is a standard breaker box in the porch area by the front door.

The plan was to feed off that with standard electrical cable, through the house to the back door where I would install a secondary breaker.

Off this secondary breaker I would run 50 metres of SWA 3 core cable that will run outside and buried under the gravel drive to the garage.

That cable would meet a fused connector block in the garage, and then wiring to a light junction box to which GU10 light bulb cup holders would be connected.

I want to install 8 spot lights of LED type that are 8 watts per bulb and I estimate about 1.6 Amps each so 12.8 Amps total.

The current rating of the cable is 23 Amps so I'm good there.

Do I need another breaker inside the garage or is fused block and the breaker by the garden door sufficient?

Obviously I want to stay within regulation, but remain as low cost as possible.

Any information on this would be welcome.

Cheers.

The bits I intend to buy
Indoors 3 core cable - This
Breaker box - This
Outdoors 3 core SWA cable - This
Fused Terminal Blocks - These
Light fittings - These
Lights - These
 
Where to start mate. You wouldn't need a secondary breaker inside the house, just some form of connection between the twin and earth (not flex as you linked to), to SWA. I would consider running a slightly larger cable to make the job more worthwhile (ie. you could stick a couple sockets in there too). Your demand estimation is way off. You would also need to consider voltage drop at that distance. I'd also be sticking a small fuseboard inside your garage (similar to your linked "breaker box"). Plus your light fittings aren't fittings, only a part of a fitting (and not really the type you would want for "working light" output.

I'd suggest getting a quote from a local electrician, post up your location and someone is bound to be near you. They might let you do some of the "donkey work" yourself to save cost.
 
You first need to know what earthing system you have at the house (TN-S / TNC-S / TT) as different requirements would be needed for each system. In fact there are far more considerations that need to be taken into account design wise, and your design as far as i can see, doesn't meet those of BS7671

Buried SWA cable needs to be at an absolute minimum of 450mm (ducted) to 500mm (direct buried) depth (depth of 2 X spade). It is also unlikely that you will have the necessary skills to terminate the SWA cable into the required glands without damaging the cable. ....And 1.5mm 3 core SWA cable, is a crazily small size to use over a 50m run.

To be honest This is ''NOT'' a DIY project, so get this job done by a competent scheme registered electrician who will also be able to certify/notify the installation . As Resu suggests, ask for quotes that reflects you doing the real donkey work, such as the trenching/backfilling and helping with the cable laying etc. You will save at least £250 in LABC notification charges alone, and be confident that the installation is correctly and importantly, ...is ''Safe''. It's a No Brainer as far as i can see!!
 
Last edited by a moderator:
the lads are correct this isn't a job for diy.
first consult with a spark in your area and go over your plans with him.
some of the work might be able to be done by you and may save you a bit.
but again this decision is best made by the spark.
its a matter of safety and legality so its in your benefit to have it done properly
 
I agree with the others mate, this sort of installation is far too much for a DIYer you have admitted you are not an electrician, get one in to give you a quote and more importantly peace of mind, don't know if you have family or friends in the house or garage, but doing it your way would put them a t risk, please get someone in who knows what they are doing.
 
I want to install 8 spot lights of LED type that are 8 watts per bulb and I estimate about 1.6 Amps each so 12.8 Amps total.
I don't quite follow that part, 8W at 230V is around 34mA. Eight lights, each 8W, would be around 270mA. Where does your 1.6A come from?

Tony S
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
DIY - Garage lighting
Prefix
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
ikodel,
Last reply from
aesmith,
Replies
6
Views
1,985

Advert