- Reaction score
- 322
Here’s the scenario:
240/480V split phase, rural overhead, ‘Farm’ supply.
From the main house Hager DB, two ways are used to supply 50A, both phases, on 16mm2, to a sub main DB in the workshop.
Is it OK to use two separate 50A Type C MCBs in the DB (cheap and available) rather than a 2-pole 50A MCB? (Expensive and very difficult to source).
No (old, exotic) 480V two-phase equipment will ever be used in any part of the installation, so there’s no question of failing to disconnect the phases substantially at the same time as is required for polyphase equipment.
The only reason in having both phases in the workshop is for load balancing.
The biggest breaker in the workshop is a 32A Type B, so the only chance of the 50A C’s ever tripping because of a fault would be cable damage, which is extremely unlikely.
The twin breakers would be clearly labelled as both supplying the single workshop DB, which itself would be labelled as having a twin source of supply.
I feels a bit wrong but is it OK electrically, or regulation-wise?
This is effectively two, separate, 240V supplies in a single box. This is so rare that the regulations appear silent on the matter.
Opinions?
Cheers, Mark
Opinions?
Cheers, Mark