Discuss Do 2-phase (split phase) lines ALWAYS need to be switched together? in the Electricians' Talk | All Countries area at ElectriciansForums.net

Mark42

-
Esteemed
Patron
Reaction score
322
Here’s the scenario:

240/480V split phase, rural overhead, ‘Farm’ supply.

From the main house Hager DB, two ways are used to supply 50A, both phases, on 16mm2, to a sub main DB in the workshop.

Is it OK to use two separate 50A Type C MCBs in the DB (cheap and available) rather than a 2-pole 50A MCB? (Expensive and very difficult to source).

No (old, exotic) 480V two-phase equipment will ever be used in any part of the installation, so there’s no question of failing to disconnect the phases substantially at the same time as is required for polyphase equipment.

The only reason in having both phases in the workshop is for load balancing.

The biggest breaker in the workshop is a 32A Type B, so the only chance of the 50A C’s ever tripping because of a fault would be cable damage, which is extremely unlikely.

The twin breakers would be clearly labelled as both supplying the single workshop DB, which itself would be labelled as having a twin source of supply.

I feels a bit wrong but is it OK electrically, or regulation-wise?

This is effectively two, separate, 240V supplies in a single box. This is so rare that the regulations appear silent on the matter.

Opinions?

Cheers, Mark
 
hi
could you use a tripple pole mcb? breaking the neutral and two of the phases?
regards
gary
Hi Gary
Thanks for the comment, but as Risteard implies, split-phase is a different animal. Without going into tedious detail it arrives from the pole transformer as 2 x 240V phases at a 180 degree phase angle, therefore 480V phase-to-phase.

I’ve used a standard Hager TPN board, commoning L2 & L3 to save ways.

Therefore the panel ways go L1-L2-L2 … L1-L2-L2 … L1-L2-L2 … and so on.

Using a standard 3-pole breaker would ‘waste’ the second L2, be untidy, and potentially confusing. I may just order a 2-pole breaker, but since I have plenty of single pole MCBs which are very cheap, I’m still tempted to use two of them instead. I really want to know what the regulatory issues are.

Cheers

Mark
 
hi

done many split phase installations but never on a tp&n db and can see what you are saying regarding the 3rd pole, what i normally do is put a tp mcb in a seperate enclosure at origin and then feed out from there switching l1,l2 & neutral. i think in your case maybe a dp mcb would be best.

regards
gary
 
You need to be careful with split phase on a 3 phase db as the maximum rated voltage of the db may be exceeded ie. 480V + permitted 10% = 528V.
 
You need to be careful with split phase on a 3 phase db as the maximum rated voltage of the db may be exceeded ie. 480V + permitted 10% = 528V.
Hi
Yes! Exactly, I'd thought about that, and it's why I joined this forum looking for opinions and advice four weeks ago:

http://www.electriciansforums.net/c...-switchgear-used-480v-split-phase-ok-not.html

Is it generally done or not?
Note that the DNO's equipment, including a TPN meter and radio-teleswitch (both with only two phases connected) is all marked up as 230/400 - 240/415 but is of course running at 240/480 in this case.
Nothing's burned down yet :) But is it 'legal'?

Cheers, Mark.
 
Hi Mark

Had a quick read of your thread.

Personally i would install 2 metal clad consumer units stacked together.
 
hey:D

double pole c50s shouldn't be hard to get -i used a load of DP mcbs c63 etc on transformer work lately


a DP isolator may do if you have switch-fuse on the supply side of sub-main

be careful if you have to switch neutral as well (all lives) -it must break last on the split-phase supply
a 3-pole mcb can't be used for this imo

practically all tn-c-s here(including outbuildings/sub-main boards)so it's less complicated
 
Last edited by a moderator:
hey:D

double pole c50s shouldn't be hard to get -i used a load of DP mcbs c63 etc on transformer work lately


a DP isolator may do if you have switch-fuse on the supply side of sub-main

be careful if you have to switch neutral as well (all lives) -it must break last on the split-phase supply
a 3-pole mcb can't be used for this imo

practically all tn-c-s here(including outbuildings/sub-main boards)so it's less complicated


hi there

what is the reason for breaking the neutral last on a split phase system? sorry if im missing the obvious..

i got annual nic inspection next week and one of the jobs have this set up.... i wonder if he will pick up on it?

regards
gary
 
didn't mean to be definitive-i'm assuming the standard 3 pole switch/mcb are not allowed (for all lives)

in case the center tap is lost momentarily

we don't switch them here
 
Last edited by a moderator:
...Personally i would install 2 metal clad consumer units stacked together.
So might I had I known the planned upgrade to ‘normal’ three phase was going to be priced by the DNO at £20,000! (and hence the plan be swiftly abandoned).

I’d already bought and fitted three Hager TPN boards.

Plus I need 40+ SP ways in the main house board, with many RCBOs, so I fancied a bigger commercial panel anyway for ease of wiring.

But I’m also not wholly comfortable with the 480V issue. But overvoltage is rare here – it’s normally the other way - especially when my goose farmer neighbour switches on all his incubators.

Although I’m hoping that there is such tolerance built into modern designs and materials it should be fine. I mean, modern plastic insulation can withstand thousands of volts for decades before breaking down. (Can’t it?)

double pole c50s shouldn't be hard to get -i used a load of DP mcbs c63 etc on transformer work lately
a DP isolator may do if you have switch-fuse on the supply side of sub-main
be careful if you have to switch neutral as well (all lives) -it must break last on the split-phase supply
a 3-pole mcb can't be used for this imo
practically all tn-c-s here(including outbuildings/sub-main boards)so it's less complicated
This installation is all TN-C-S as well.

Yes, I’ve fitted a new TP switchfuse upstream, with solid neutral, fed from the meter tails. It’s just under three meters from there to the main DB (space is tight otherwise) so I felt better protecting (and switching) the DB supply cable (4 x 25mm SWA) that way. It also enables the barn sub-main to come directly from this switchfuse rather than from DB1. Also it eases the changeover from old to new installation, with much less working live.

But since the switchfuse is 100A, I’d rather not use only a DP isolator downstream for the workshop supply, even though it’s on 16mm. It’s a good idea, and I have plenty of old isolators in my junk box, but I like the idea of having 50A protection downstream. Plus, strictly, it’s no doubt a requirement due to the CSA reduction.

By hard-to-get I meant not listed anywhere online (I usually use TLC), so I may - heaven forefend - have to pick up the phone and actually talk to a real person! Maybe next week.

Gary – I’m not sure I understand you. Do you really mean a 3P over-current MCB, or an isolator (ie just a switch)? Surely you can’t run two phases plus neutral through a 3P MCB? This may be reaching the outer edges of my understanding, but would the third phase not be trying to monitor and protect the ‘reverse’ neutral current? It feels odd to me.

Thanks for all the advice gentlemen; it’s much appreciated.
 
ya for tn-c-s you only need DP mcbs/switching on supply/distribution for split-phase

and SP for 230v final circuits




i may be overly cautious about switching star points/centre taps

3-pole mcb may not be an issue if all poles make/break substantially together-maybe someone can confirm?

(if the centre tap is lost on the supply/distribution side the 480v may divide unevenly across the loads)

prob not a great idea feeding the 2 boards from the 'main' TPN switchfuse imo -i would fit separate switchfuse for the sub-main and an isolator at the sub-board for tn-c-s

assuming you can export the earth in your case(we don't convert sub-mains to TT here at all)
 
Last edited by a moderator:
So might I had I known the planned upgrade to ‘normal’ three phase was going to be priced by the DNO at £20,000! (and hence the plan be swiftly abandoned).

I’d already bought and fitted three Hager TPN boards.

Plus I need 40+ SP ways in the main house board, with many RCBOs, so I fancied a bigger commercial panel anyway for ease of wiring.

But I’m also not wholly comfortable with the 480V issue. But overvoltage is rare here – it’s normally the other way - especially when my goose farmer neighbour switches on all his incubators.

Although I’m hoping that there is such tolerance built into modern designs and materials it should be fine. I mean, modern plastic insulation can withstand thousands of volts for decades before breaking down. (Can’t it?)


This installation is all TN-C-S as well.

Yes, I’ve fitted a new TP switchfuse upstream, with solid neutral, fed from the meter tails. It’s just under three meters from there to the main DB (space is tight otherwise) so I felt better protecting (and switching) the DB supply cable (4 x 25mm SWA) that way. It also enables the barn sub-main to come directly from this switchfuse rather than from DB1. Also it eases the changeover from old to new installation, with much less working live.

But since the switchfuse is 100A, I’d rather not use only a DP isolator downstream for the workshop supply, even though it’s on 16mm. It’s a good idea, and I have plenty of old isolators in my junk box, but I like the idea of having 50A protection downstream. Plus, strictly, it’s no doubt a requirement due to the CSA reduction.

By hard-to-get I meant not listed anywhere online (I usually use TLC), so I may - heaven forefend - have to pick up the phone and actually talk to a real person! Maybe next week.

Gary – I’m not sure I understand you. Do you really mean a 3P over-current MCB, or an isolator (ie just a switch)? Surely you can’t run two phases plus neutral through a 3P MCB? This may be reaching the outer edges of my understanding, but would the third phase not be trying to monitor and protect the ‘reverse’ neutral current? It feels odd to me.

Thanks for all the advice gentlemen; it’s much appreciated.


yes a tp mcb as overcurrent protection. ive done this on two jobs and had no problem but not saying that its a normal way of doing it. normally put L1 - N - L2 in the breaker and the neutral will never exceed the line current being that it is split phase. hope i am not confusing matters.

regards
gary
 
yes a tp mcb as overcurrent protection. ive done this on two jobs and had no problem but not saying that its a normal way of doing it. normally put L1 - N - L2 in the breaker and the neutral will never exceed the line current being that it is split phase. hope i am not confusing matters.

regards
gary

i could well be wrong as i'm not overly familiar with TT
it may indeed be ok for all llives to switch simultaneously for TT- i know that for isolators they may make first /break last

a lost neutral on the split-phase could cause a lot of problems
 
SSE install their own REC 4 isolator after the service cut out / polyphase meter on split phase. Two ways are used as L1 and L2, L3 is blanked off and the neutral is a solid non switched link. They will fit a "normal" REC 4 but will not be held responsible for any damage caused to the system if the neutral breaks first or makes last - their view is that the consequencies however small of getting momentary - or worse - 460V to earth (in a 230-0-230 tncs system) is too great to risk. I had a Hager 63A type D 3way mcb to isolate the split phase supply from a wind turbine i.e. L1, L2, neutral but since that "discussion" I have taken the neutral to a common neutral bus connection inside the mcb enclosure.
 
Thank you for a positive reply ! It is my first post and in my excitement to find something that I actually had knowledge of I completely missed the date of the OP............will try harder next time :blush2:
 
Ha Ha! Thank you for your (belated) interest, gentlemen. Yes, all sorted long ago: I used the correct Double Pole MCB. No problem to source, it was just that my usual supplier, TLC, did not list them.
Welcome, Bill - if you have a split phase install at home, I'm delighted to find someone else on here who might actually know what it is! Are you saying you NEVER switch neutrals?
 
Thank you for the welcome - I decided to err on the side of caution in the belief that the SSE may actually know what they are talking about in this instance - especially as this is a common upgrade in North East Scotland and they do a lot more split phase installs than I do (and they gave me a nice REC4) so for split phase systems I don't switch neutrals - so far it has been the correct decision !! What was also vaguely interesting was that I checked with Hager Technical regarding the mcb I fitted and they told me that Hager mcb neutrals do indeed break last, make first.........but how can you be sure without 100% QA/QC ? we are talking milliseconds...............
 
Sorry Bill, just lately we’ve had lots of resurrected threads and they tend to confuse things.
Split phase supplies can be a bit of a minefield, I got used to them working in quarries 40 odd years back.
There has been a resent thread about them, which is a bit weird in the way the DNO have done it.
 
tt system on a farm what advice would members give on fitting 300ma rcds on a split phase supply looking at pv install so type a rcd required.regards
 
0° centre tapped is normal. 180° will give 0V phase to phase and the neutral would have to be 2X phase CSA conductor.
It could be a Scott or LeBlank 90° connection

So what voltage does the PV system work on?
 
single phase inverters 3.6kw tl fitting two each protected by 100ma rcd type A, farm install.treating the install as two seperate installs g83 settings so 240v nom 1%vd design swa cable regards
 
If you are going to be feeding in to the network then you could run in to problems with 230V.
You would effectively be feeding in to only ½ of the transformer winding, it won’t be happy, neither will the DNO!

I have sent you a PM
 

Reply to Do 2-phase (split phase) lines ALWAYS need to be switched together? in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and...
Replies
23
Views
3K
Hi All, I've posted on here before about this, that time i was asking what people thought about phase converters as at that point i thought i...
Replies
14
Views
3K
I don't normally get involved with domestic work but this job is for a family member so I cant Simpley say no. the house is a large property with...
Replies
3
Views
1K
I'm fitting a small kitchen in my remote office/workshop with a limited, existing, supply (3 phase/20A MCB on a long 4 x 10mm SWA). I need to...
Replies
8
Views
2K