got a new toy ha ha clamped my new earth leakage clamp around my earth cable local to consumer and was getting 5mili amp leakage question what mainly causes the earth leakage other than computers fridges etc
 
Which one have you purchased ?
I bought a DCM305E on Friday off the Megger rep.. Not had chance to use it yet
 
it was 8.6mili amps around tails and 6 mili amps on the earth cable no computers on tv is on and fridge and freezer what else could be causing this leakage
 
anyone charging a few mobiles , (Turn off various RFC,lighting at CU)
 
If its a Tnc-s system I suppose its possible that next doors earth leakage is finding its way to the neutral via yours
 
Sadly we pay for quality (real iPhone chargers ).
Plenty of TVs DVR ,DVD players are good for an odd milli-amp.
(the old transormers are too full of copper at 50Hz-hence replaced !)
 
a friend of mine told me he uses the clamp meter for his ir tests dosent do any ir testing just calculates the ir from the leakage current he detects whats your thoughts on that says it saves him lots of time still need convincing that this is ok
 
a friend of mine told me he uses the clamp meter for his ir tests dosent do any ir testing just calculates the ir from the leakage current he detects whats your thoughts on that says it saves him lots of time still need convincing that this is ok

I use that method on jobs where I need to know the ir but can’t turn the power off
 
a friend of mine told me he uses the clamp meter for his ir tests dosent do any ir testing just calculates the ir from the leakage current he detects
Does sound dodgy ,if no one else can get same figure with 500V .
Can see where he is coming from Not having to unplug all those delicate electronics (they get tested at 380-400VDC)
 
its a good idea and would save you lots of time quick clamp and calculate and onto the next one or better still the pub quicker. would be good before a board change
 
Also you need to know that when using ac to test we will be measuring impedance and not resistance as in a dc IR text
 
Computers, SMPS, TV boxes, play stations. etc
 
  • Like
Reactions: static zap

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wirral
Business Name
Farm electrics

Thread Information

Title
earth leakage
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Farmelectrics,
Last reply from
cliffed,
Replies
24
Views
4,107

Advert