Discuss EV charger on garage CU in the UK Electrical Forum area at ElectriciansForums.net

matthew77

DIY
Reaction score
0
Hi all,
First post so appologies if this is not the place to ask.

I'm after some help after receiving conflicting advise from a couple of electricians regarding the install of an EV charger on the outside of my garage, the garage is detached from the house.
Garage is fed with 10mm2 SWA from the main CU in the house with a 40A mcb, non RCD.
Within the garage is a small CU with its own type A RCD and 3 breakers.
6A for the LED lighting, 20A for a couple of sockets and an unused 32A .
The 10mm SWA was put in place at my request a couple of years ago when I had the garage built and driveway laid. CU in the house was replaced at the same time and has a spare capacity if required.
One electrician has said the unused 32A breaker is ok to feed a charger and the SWA to the garage is suitable.
Another chap says its best to run a separate SWA from house direct to the charger.
I am reluctant to have another cable put in under the new driveway if what's already in place is suitable.
The earthing system is TN-C-S and I'm told a separate earth rod maybe required depending on the type of charger I go for.
All I need to know basically, is if the current install allowed ? or must I have a separate feed to the EV charger from the house.


Many thanks
 
The length of the 10mm2 SWA is the deciding factor, but I'd be very surprised if feeding the EV from the garage isn't absolutely fine.
Did the one who wants to run a new cable give any indication why?
 
Subject to VD and a site survey, it sounds to me like you can use the 10mm SWA as suggested. There's plenty of options on EV charger these days that will mean you won't necessarily need an earth rod.
 
Fig. 5 on page 2 of that installation guide is a bit presumptive! My own EV charge point is fed from a 36 module DIN enclosure with many more blanks than devices, and I wouldn't have been at all happy if an installer had fitted an additional enclosure.
 
Thanks for the replies.
Length of SWA is 12meters.
The chap that suggested a separate SWA to the charge point mentioned RCD selectivity but I'm not bothered if it takes out the garage rcd upstream from the charger. And also he said ideally the garage CU wouldn't be fed via the house CU, so Im guessing he means it ideally should be fed from the meter cupboard using henley blocks.
I guess they just have different opinions rather than one being wrong and the other right.
As long as the install I have now doesn't sound like its against any regulations then I'm happy.
Should the garage door be bonded ? Its an electric roller shutter.
 
You said that the garage feed was just through a MCB, and not a RCD, so there is absolutely no reason for a separate box next to the existing CU. Ideally, the garage feed would be via a cartridge fuse rather than a MCB, but that's a minor point.
 
Don't know of any cartridge fuses for consumer units these days, but MEM produced them for their boards a few years ago. Often fitted them for the likes of storage heaters and immersion heaters - things that needed short circuit protection but not overload protection.
The advantage of a fuse feeding the garage is discrimination. A short circuit in your garage, rather than overload, will trip the local MCB, and quite likely the one in the CU as well, but a fuse is much more likely to survive
If you did fit a separate box to feed the garage, it should be a switchfuse, not an enclosure with a main switch and a MCB.
Don't need to do calculations for 12m of cable. It will be well within limits. As a general rule, it's when you get to about 50m that you need to do the calculations.
 

Reply to EV charger on garage CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
784
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock