so im trying to work out the minimum size main earth for main supply ze=0.11 its a tncs supply i would say k=143 and for the main consumerunit i would say its 5 second disconection time so
230/0.11=2091
so doing the caculation i get 32.9mm and this cant be right what am i doing wrong it must be T
a bs 1361 will go quicker than 0.1 s at that fault curent.
so taking pg 244 time/current characteristics for 1361 60 a fuse at 5 seconds is 330A so doing the calc again i get 5.16mm this is better but what is right or for a consumerunit disconection time is it 0.4
please help i done it on a pir with a 6mm main earth which i doubled up to 12mm but minimum size is 5.16mm now this is safe just not conforming to bs7671 2008


You are incorrect with your 5 second disconnection time. The disconnection time is worked out by finding the fault current and using the time current curves in the Green book.
 
This equation allows you to calculate the CPC size only this must be used as a part of a cable calculation not just by its self. As you also need to take into account your R1 + R2 & Zs calcs.
You can not use this for main earth or bonds. You need the green book for that.
 
Just a quick question on the rules in maths if this thread is still live. In the equation do you apply the sq root before before deviding by the K factor ? If you do the sq root last, the answer is vastly different.

Mick
 

Reply to Example of use of Adiabatic Equation. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
814
Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
550
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock