Evening All,

Strange one so after a bit of advice. Got called to a customer this evening who had their boiler repaired after the circuit board got fried supposedly after a power cut when the supply was restored. They were told they needed a switch fused spur fitted as there was no way of isolating the boiler. I turn up to fit sfcu and notice that the supply to boiler is via a 1mm three core and earth. The supply is from 32 amp mcb with Rcd as main switch on Tt. I told the client I am not going to fit fcu until I have investigated a little further as cable is undersized and there must be a jb somewhere. while I was there downstairs lights on 2 separate 6 amp mcb start flickering Intermittently. Being Fri night i am going back sat to get the trusty tester out. Has anyone had this happen before or any suggestions what could cause the flickering. My gut is saying there Is an underlying fault that may have caused the boiler failure Not the power cut.

thank you
 
Possibly bad connection on tails or incoming cable? If not could even be bad connection where incoming cable is jointed outside.
 
  • Like
Reactions: DPG
What kind odd lamps?

Filament and LED can flicker under different conditions.

Is it only one type flickering.

Is the flickering random or more regular

Very likely a loose neutral if 2 circuits are affected.
Other appliances may not show a fault the same as simple lights will, but it could be affecting every circuit.

Good luck finding it.
 
Hi all thanks for help, loose neutral at main switch all sorted now .
Not too serious then. 🧐

Glad you found it before things started melting.
 
  • Like
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South East Kent

Thread Information

Title
Flickering lights on separate circuits
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Rockomuir,
Last reply from
littlespark,
Replies
4
Views
1,567

Advert