Discuss Help me work out volt drop please.... in the UK Electrical Forum area at ElectriciansForums.net
Gringoking88
Hi all,
I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone please help me understand how to get the answer as I just cant seem to work it out!
Thank you advance!
Voltage drop of a single-phase distribution circuit supplying a power distribution board in a remote building is to be verified as part of the periodic inspection and testing within a workshop complex. The installation forms part of a public 400/230 V TN-S system.
The circuit has a measured R1+Rn value of 0.15 Ω and an Ib of 60 A. The circuit protective device has an In of 80 A, see Figure 5.
What is the maximum acceptable voltage drop for this distribution circuit if the highest circuit voltage drop on DB-3B is 5.0 V?
IGZvA3KxNPILPwjwr8XDN6mu-02bn3XflSgHbYpnFZi6bk5z1YYIdwA4J_53ocLYeLgwWyhtD-eV5K0sjWKMOKxRdhTVTf9WlmLKhnV35PdzPiOGmVnEBkMK8S2DwOLQudvhiNiVb77KGBz5sQ
a) 11.5 V
b) 6.9 V
c) 6.5 V
d) 1.5 V
How far have you got? Have you found the formula for voltage drop?
Total Maximum permitted VD from Main DB to end of final circuit from DB3 = (say5%)
Therefore max permitted VD on distribution circuit = 5% - 5.0volts (from question) =
Im sorry this is probably the bit that is confusing me, could you explain please?
The maximum permissible VD at the farthest point of any circuit (except a lighting circuit) is 5% or 11.5 volts
The volt drop on one of the circuits from DB3 is already calculated to be 5volts (in question)
Therefore 11.5 - 5 = 6.5vots permitted to be 'dropped' on distribution circuit.
As #6, too much information given beforehand.
So it's asking for maximum permissable v.d and its single phase so 5% of 230v = y (This is the total v.d you are allowed). You are told that a circuit from DB3 has a v.d of 5v so y - 5v = max v.d allowed for the distribution circuit.
simple. you are allowed 5%, or. 11.5V in total . as the DB3 has a VD of 5V already, your distribution circuit max. VD id 11.5 - 5.0 =6.5V. answer (c),
People have already responded to your other thread.
Many years ago I set the questions for the Fellowship entrance to one of my Institutes, it was always the older, supposedly more intelligent candidates that failed and always for the same reason, not reading the question correctly, ergo if you fail you are more intelligent. ?
Many years ago I set the questions for the Fellowship entrance to one of my Institutes, it was always the older, supposedly more intelligent candidates that failed and always for the same reason, not reading the question correctly, ergo if you are old you are more intelligent. ?
corrected for you.
The problem is that I have so much information stored in my Brain that some of it has to leave to allow new information to come in, that's my excuse for being forgetful and I am sticking to it.
Reply to Help me work out volt drop please.... in the UK Electrical Forum area at ElectriciansForums.net
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Select (Scottish) Certification Scheme Question on volt drop from 2391
Hi all, I have worked out the volt drop on other questions using the formula mVxAxM. had no issues, but this question below has just fried whats...
6K