Hi Regarding the heater and the 4 wires .Will I be able to put a plug on this heater.
What will I do with the fourth black wire ?
I have never come across this before just need some advice please
 
The manual tells you about the connections:

1 Neutral conductor = blue
2 Live = brown
3 Earth conductor = green/yellow
4 Control cable = black

There are 3 possible ways to connect the appliance:

- Appliance connection without control cable
Unregulated appliance. The control cable is not connected. In this case, insulate the control cable.

- Temperature setback via control cable
To reduce the temperature to the set setback temperature, the black control cable is activated via an external electronic contact (e.g. a time switch).

- Control cable connected to external control unit
The appliance can be connected to any control unit that issues the following waveforms as control signals.
[See table in the manual for more info]
 

Reply to I have a stiebel CNS 300 wall heater. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top