Have customer who has staircase led lights if switched on and off within few seconds the rcbo trips, if switched on left for few seconds then switched off no problems, i am assuming the surge by transformer is issue ?
 
Indoors? Is the rcbo dedicated to this, or is it an up or down lights rcbo? 6A? Or something else?
I'm a bit surprised if it's a current surge, but suppose that's possible. Maybe earth leakage for some reason?
Any chance of trying a different driver, or is it a mystery bespoke setup!
 
Let us know how it looks. LED staircase for indoors.... interesting
 
It would be unusual for this type of lamps to have an earth connection, so I suspect it's an earth -neutral fault on another part of the circuit, or any circuit protected by the same RCD.
Edit: I see the OP says RCBO, so it could be inrush, but I'd IR test first.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sajeel

Arms
~
Joined
Location
London

Thread Information

Title
led staircase lights
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
led lights

Advert

Thread statistics

Created
sajeel,
Last reply from
brianmoooore,
Replies
3
Views
494

Advert