Probably barking up the wrong tree here but those Henley/connector blocks look odd, the wires coming out at least; outer 2 appear to go to the switch fuse, inner 2 to the isolator - would have thought it'd be 2 left, 2 right ,but then I remembered its line & neutral so should it not be a case of 1 & 3 to switch fuse (or isolator) and 2&4 to either the isolator (or switch fuse) as it stands you've got 1&4 used together at the switch fuse and 2&3 at the isolator.

As I say I'm probably wrong but it didn't look right to me.

It doesn't matter, the service connector blocks are just commoning blocks and don't have any specific terminal designations. Whilst it would be nice for each one to be connected in logical order it doesn't make any difference functionally.

The bigger question as far as that isolator is concerned is why the smaller CU has been connected before the DP isolator? The whole point of having a seperate isolator fitted is to be able to isolate the whole installation from the incoming supply.
 
It doesn't matter, the service connector blocks are just commoning blocks and don't have any specific terminal designations. Whilst it would be nice for each one to be connected in logical order it doesn't make any difference functionally.

The bigger question as far as that isolator is concerned is why the smaller CU has been connected before the DP isolator? The whole point of having a seperate isolator fitted is to be able to isolate the whole installation from the incoming supply.
If you are talking about the small left hand side CU that’s just another isolator for the outhouse CU.

this wasdone so I could stop either CU supply independently. I believe it’s in a meta box because the armoured cabled to be installed properly needs a proper casing to connected onto via a gland.
 
The bigger question as far as that isolator is concerned is why the smaller CU has been connected before the DP isolator? The whole point of having a seperate isolator fitted is to be able to isolate the whole installation from the incoming supply.
Come on dave, think about it…….it's just another isolator doing the same thing for part of the installation...fused down.
 
If you are talking about the small left hand side CU that’s just another isolator for the outhouse CU.

this wasdone so I could stop either CU supply independently. I believe it’s in a meta box because the armoured cabled to be installed properly needs a proper casing to connected onto via a gland.

Yes I'm talking about the small CU to the left which has been connected before the plastic supply isolator so that you have no single point of isolation for the entire installation, defeating the object of having the plastic isolator fitted in the first place.

You can isolate each CU via their main switch independantly without that isolator,
[automerge]1577476035[/automerge]
Come on dave, think about it…….it's just another isolator doing the same thing for part of the installation...fused down.

I'm thinking about it and can't see it.
It's also not fused, that is just a wylex REC2 100A DP switch in a plastic box
 
Yes I'm talking about the small CU to the left which has been connected before the plastic supply isolator so that you have no single point of isolation for the entire installation, defeating the object of having the plastic isolator fitted in the first place.

You can isolate each CU via their main switch independantly without that isolator,
[automerge]1577476035[/automerge]


I'm thinking about it and can't see it.
It's also not fused, that is just a wylex REC2 100A DP switch in a plastic box
??‍♂️ Honestly don’t know it’s how it was
Yes I'm talking about the small CU to the left which has been connected before the plastic supply isolator so that you have no single point of isolation for the entire installation, defeating the object of having the plastic isolator fitted in the first place.

You can isolate each CU via their main switch independantly without that isolator,
[automerge]1577476035[/automerge]


I'm thinking about it and can't see it.
It's also not fused, that is just a wylex REC2 100A DP switch in a plastic box
no idea mate, I mean I could switch both off and isolating both CU from any supply? The only time I think that would ever need to happen would of changing CU? Which fingers crossed would be never
 
I'm thinking about it and can't see it.
It's also not fused, that is just a wylex REC2 100A DP switch in a plastic box
That's feeding the main CU. Your 'small CU to the left' is isolation for the outhouse....fused, I'll wager.......and I'd sooner have that as isolation than a cheap plastic one.
 
1) Mrs turned the iron, but no light, so I thought the switch was off, went to turn it on, but it was on You'll be surprised what they will do to get out of doing the housework :p
2) Kids coming running in saying wifi isnt working This is actually a great way of finding out how many kids are in the house


Not that I know much but have you tried the iron since?
 

Reply to Lost power but NO RCBO tripped in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
795
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
952
I had a 6amp RCBO feeding a 2.5mm radial ( temporary measure) It tripped, as I expected would But once tripped, all the other circuits went...
Replies
25
Views
2K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
862
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock