I am currently testing a ring circuit with an r1 of 1.12 an rn of 1.12 and an r2 of 1.80
I have carried out my figure 8 test only to find that i have varying readings at the sockets between 0.40 and 0.80. How is it that I could be getting a low reading such as 0.40 with no parallel paths. I have made double sure I have carried out the figure 8 test correctly. Could this indicate a ring in a ring?
 
what would you like it to be? did you zero your test equipment?
 
  • Like
Reactions: 2 people
from you r1 and r2 readings, you would expect R1+R2 at each outlet to be about 0.75ohms.
 
Have you tried retesting the end to end values and making sure you have a good connection to the cable ends, a variation of 0.16 / 0.32 Ω could by caused by contact resistance or loose lead connections.
I assume the values you are measuring are for the r1 / rn figure 8?
Alternatively you could still have the ends the wrong way round and it is just a long run to the first socket.
What results do you get if you swap the connections round the other way?
 
deleted due to incriminating myself for being stupid.
 
Last edited:
You can get a low reading when doing a fig 8 test if you have a boiler circuit that has crossbonding, even with the load disconnected leaving the earths connected will give a lower reading as you aproch the spur. Look for something like that. Even a forgotton washing machine plunged in will cause this.
 
  • Like
Reactions: 2 people
You can get a low reading when doing a fig 8 test if you have a boiler circuit that has crossbonding, even with the load disconnected leaving the earths connected will give a lower reading as you aproch the spur. Look for something like that. Even a forgotton washing machine plunged in will cause this.
It is surprising how many "testers" forget that disconnecting items from a RFC,may include what you have discussed,and leaving conductors,other than the line,still connected,can affect results. If only every RFC was as drawn in a text book...just posted about one i went to, a mixture of upstairs and downstairs radials,joined at one MCB,with at least two interconnections,and spurs going everywhere...extractors,boosters,garden lighting and a whole recently fitted kitchen...marvelous :pirate:
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Low R1+R2
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Thread Tags

Tags Tags
r1+r2

Advert

Thread statistics

Created
Bazultra,
Last reply from
PEG,
Replies
8
Views
2,539

Advert