MAX LOAD FOR DOUBLE UK DOMESTIC 3 PIN SOCKET?

Discuss MAX LOAD FOR DOUBLE UK DOMESTIC 3 PIN SOCKET? in the UK Electrical Forum area at ElectriciansForums.net

dimmy

-
DIY
Reaction score
0
Hi
With a standard 13 amp domestic uk 3 pin socket the max load is 13 amps i believe?. So does this mean that a DOUBLE socket would have a max load of 26 amps....OR is a double socket still only 13 amps?. In one part of the double socket i have ( on a 3 way adapter) a tv, a blu ray player and a router..which are all light loads. Can i plug in a 2kw portable air conditioner into the free 3 pin socket on the other half of the double socket?...it says in the manual don`t use an extension lead for the PAC....any idea why not?...i have a 2 metre 13 amp extension lead but am wary of using it...many thanks
 
I see no issue with this loading of a double socket.
I suspect it says not to use any extension lead because it’s the easiest way to stop people using an undersized extension lead or a coiled lead without uncoiling it fully. A correctly sized and rated extension lead won’t be a problem in reality, 1.25mm or 1.5mm cable would be suitable.

As far as I know 13A double sockets are required by the British standard to safely handle a load of 20A between the two sockets. With the standard test being a 13A load on one side and a 7A load on the other.
 
I see no issue with this loading of a double socket.
I suspect it says not to use any extension lead because it’s the easiest way to stop people using an undersized extension lead or a coiled lead without uncoiling it fully. A correctly sized and rated extension lead won’t be a problem in reality, 1.25mm or 1.5mm cable would be suitable.

As far as I know 13A double sockets are required by the British standard to safely handle a load of 20A between the two sockets. With the standard test being a 13A load on one side and a 7A load on the other.
It is a recommendation that loads of 2KW and above should be on their own separate circuit.
 
The ratings on portable air conditioners are bull anyway. See this one...

https://www.amazon.co.uk/TROTEC-PAC-2000-Local-Conditioner/dp/B00U65A9M8

Says it has a "maximum cooling capacity of 2.0 kW", but then, in the spec, it says "Power consumption max.: 0.79 kW"!! :eek:

And here's a 5.2kW one which comes with a normal 13A plug, because it only uses 1.8kW in reality!! :rolleyes:
PAC18H - 18000 btu Portable Air Conditioner - £550.00+vat - https://www.climachill.co.uk/product/pac18h-kyd52-18000btu-portable-air-conditioner-cool-heat/
 
HVAC units usually involve a compressor. These can have a high inrush current. They also have a limiting device to prevent restarting until the pressure in the system equalises. Which is why if you have unplugged one you should wait a few minutes before plugging back in, (to avoid a pressure lock and burning out the motor).

Manufactures know that a BS7671 socket and the lead and plug supplied will not produce a voltage drop that would give any problems. However an extension lead of a given length could cause stop start problems and motor damage. So they play safe and say no extensions.
 
Not really I merely said that BS7671 makes a recommendation that fixed loads of 2 KW and over are connected on a dedicated circuit
 
Recommended by who and where?

Of that is the case then why on earth do we have socket circuits with more than one outlet on each circuit?

Would you install a separate circuit for a kettle, toaster, hair dryer etc etc ?
Fixed loads Dave, fixed Loads.
Appendix 15A iii
 
it says in the manual don`t use an extension lead for the PAC....any idea why not?............
Ususlly because excessive volt drop across the lead during start current can cause premature compressor failure and there's lots of poor quality extension leads around. If it's a 2.5mm lead of a good brand name and relatively short in length it should be fine.
 
Double sockets have a rating of 13A on them don’t they?
I’ve ben through most makes and non of them take 12.5A on a thermostatically controlled deep fat frier used for 6 hours a day for more than a month or two. Nor do BS1363 plugs or BS1363A plugs!
 

Reply to MAX LOAD FOR DOUBLE UK DOMESTIC 3 PIN SOCKET? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock