HappyHippyDad

~
Esteemed
Arms
Supporter
Dec 18, 2011
5,378
6,731
405,788
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
My customer has had a completely new supply installed to his garage. The DNO has not put a fuse in the cut out though. I'm guessing he needs to contact the DNO to discuss? I realise it would be very easy to pop a fuse in, but apart from this not being allowed, I also wouldn't know the size of the supply cable and therefore have no way of knowing which size fuse is safe.

Is it usual for the DNO to leave the fuse out?

Also, they have not put a meter in. I realise the meter is the domain of the electricity supplier, but I thought with a new supply the DNO fit one. Have I got this wrong? If so, does the customer simply choose a supplier and then they fit a meter? (Meaning the supplier has to enter the cut out)

lastly, it is PME. No earth cable has been terminated into the cutout. Is this something the DNO should have done (and perhaps left in an earth block). Not sure how else I am going to get the earth installed, without removing the fuse to get to the earth terminal.

Thanks all.
 
Western Power don't fit the meters for our new supplies, it's down to the provider. They have always left the fuses in though. They also make a note of the Ze and mark up rotation if it's three phase.

For the earth there is normally a blind gromit on the right hand side of the cut out you can pull out to access the neautral/earth block.
 
Western Power don't fit the meters for our new supplies, it's down to the provider. They have always left the fuses in though. They also make a note of the Ze and mark up rotation if it's three phase.

For the earth there is normally a blind gromit on the right hand side of the cut out you can pull out to access the neautral/earth block.
Thanks David,

Looks like it's just the fuse part that is a little unusual then. I'll ask him to contact DNO to get fuse fitted (and seals installed!)

I forgot about the grommet. I'm still thinking of the slightly older cutouts where you had to remove the fuse in order to get to a screw to remove the cover... in order to get to the earth terminals. You're quite right, there is a grommet (see pic).

Cutout.jpg
 
One last thing.. Does the 100A written on the cutout relate to the max rating of the cutout (like an RCD) or the fuse size?

The reason I ask is because I have always thought it relates to the fuse size, because directly below it states Type IIb which is the model of the fuse. However, if they haven't even put a fuse in, perhaps it is a max rating?
 
One last thing.. Does the 100A written on the cutout relate to the max rating of the cutout (like an RCD) or the fuse size?

The reason I ask is because I have always thought it relates to the fuse size, because directly below it states Type IIb which is the model of the fuse. However, if they haven't even put a fuse in, perhaps it is a max rating?
Do you know what customer requested / ordered?
As you say, the labelling can't be relied upon.
 
One last thing.. Does the 100A written on the cutout relate to the max rating of the cutout (like an RCD) or the fuse size?

The reason I ask is because I have always thought it relates to the fuse size, because directly below it states Type IIb which is the model of the fuse. However, if they haven't even put a fuse in, perhaps it is a max rating?
WPD should put the correct sticker on the holder when they fit the fuse.
 
  • Optimistic
Reactions: brianmoooore
One last thing.. Does the 100A written on the cutout relate to the max rating of the cutout (like an RCD) or the fuse size?

The reason I ask is because I have always thought it relates to the fuse size, because directly below it states Type IIb which is the model of the fuse. However, if they haven't even put a fuse in, perhaps it is a max rating?
I wouldn't have put a fuse in either, not with having no meter or CU.
 
  • Agree
Reactions: BenCos18
The 100A is the max rating of the carrier. Various sizes of fuse are avalable 100/80/60 are the most common but you get much smaller sizes as well for bill board, phone kiosks, lighting etc.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
New supply to garage. DNO have not fitted fuse.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
R-fur,
Replies
7
Views
1,892

Advert