Hi, i'm currently doing my Level 3 design project and it's going to be tricky with the coronavirus and lack of contact with Tutor and other students.

Its the Hotel Swimming pool one

and I have to select luminaries for the cafe pool.

I haven't chosen my luminaries but I'm thinking to do it all with SELV 12V now how do I do cable calculations and Max Demand for a Selv circuit? Also what cable should I use, I was thinking FP200 as it's a public area is this ok for Selv?

You may laugh at my suggestion but any help would be great.
 
This is what the regs say about protection for safety and the application of protective measures against electric shock.

"702.410.3.4.3 Zone 2
One or more of the following protective measures shall be employed:
(i) SELV (Section 414), the source for SELV being installed outside zones 0, 1 and 2. However, it is permitted to install the source for SELV in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1

(ii) Automatic disconnection of supply (Section 411), using an RCD having the characteristics specified in Regulation 415.1.1 NOTE: Where a PME earthing facility is used as the means of earthing for the electrical installation of a swimming pool or other basin, it is recommended that an earth mat or earth electrode of suitably low resistance, e.g. 20 ohms or less, be installed and connected to the supplementary protective equipotential bonding.

(iii) Electrical separation (Section 413), the source for electrical separation supplying only one item of current using equipment and being installed outside zones 0, 1 and 2. However, it is permitted to install the source in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1."

If you're worried about things like IP rating, you can get away with IPX2 fittings so you don't even need anything special unless it's outside or you're going to jetwash them.
 
Upvote 0
Assuming the Ceiling is Zone 2 we don't even know the height of the room and if there's a diving board it would have to be even higher I.e the ceiling or the walls could be Zone 1 needing SELV.
Looking at the Drawing scale midway up the walls must be Zone 1 breaching the Regs if you put LV lights there.
This is what the regs say about protection for safety and the application of protective measures against electric shock.

"702.410.3.4.3 Zone 2
One or more of the following protective measures shall be employed:
(i) SELV (Section 414), the source for SELV being installed outside zones 0, 1 and 2. However, it is permitted to install the source for SELV in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1

(ii) Automatic disconnection of supply (Section 411), using an RCD having the characteristics specified in Regulation 415.1.1 NOTE: Where a PME earthing facility is used as the means of earthing for the electrical installation of a swimming pool or other basin, it is recommended that an earth mat or earth electrode of suitably low resistance, e.g. 20 ohms or less, be installed and connected to the supplementary protective equipotential bonding.

(iii) Electrical separation (Section 413), the source for electrical separation supplying only one item of current using equipment and being installed outside zones 0, 1 and 2. However, it is permitted to install the source in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1."

If you're worried about things like IP rating, you can get away with IPX2 fittings so you don't even need anything special unless it's outside or you're going to jetwash them.
 
Upvote 0
The celling of the pool is approx 2.7/2.8m from the floor and therefore is outside of zones. The walls east, north and west are zone 2. The south wall with changing rooms is just outside the zones.
The cables in which you can use have been pre decided for you so too has the the containment method.
The only place I used selv was for the plunge pool as there's physically no other way to get lighting and had the junction box inside the pump Room.
 
  • Like
Reactions: Mark Wright
Upvote 0
The celling of the pool is approx 2.7/2.8m from the floor and therefore is outside of zones. The walls east, north and west are zone 2. The south wall with changing rooms is just outside the zones.
The cables in which you can use have been pre decided for you so too has the the containment method.
The only place I used selv was for the plunge pool as there's physically no other way to get lighting and had the junction box inside the pump Room.
Dude your right it says the ceiling is 2.4m above ffl so only just in Zone 2 Thanks
 
Upvote 0
Sorry, I made a boo boo! The 3 walls are within zone 1 not 2 (thinking of rooms with bath/shower ?), and so the south one is zone 2 just. No given height for plunge pool but as the plans show a level floor and steps leading to plunge then you can guess the celling height is more likely to be less than 2m.
As for fitting lights along the walls as suggested, why? You can use 240v across the celling which will help with that practically impossible 30m max circuit lengths
 
Upvote 0
and I think its
Sorry, I made a boo boo! The 3 walls are within zone 1 not 2 (thinking of rooms with bath/shower ?), and so the south one is zone 2 just. No given height for plunge pool but as the plans show a level floor and steps leading to plunge then you can guess the celling height is more likely to be less than 2m.
As for fitting lights along the walls as suggested, why? You can use 240v across the celling which will help with that practically impossible 30m max circuit lengths
I'm just going with Ceiling lights now but technically Zone 2 is meant to be 2.4m from the floor isn't it? Not exactly happy but......
 
Upvote 0
Haven't got books on me atm and CBA to go to van to get them ?, but I'm pretty sure that anything above 2.5m in height is outside zones. The height of the main pool is over over 2.5m to celling.
The zones go outwards, not upwards.
 
Upvote 0
Zone 2 runs from the floor to a height of 2.5m above finished floor level.
 
Upvote 0
As above you need to remember just because a wall falls within a zone its full vertical height may be outside of it.
 
Upvote 0
Zone 2 runs from the floor to a height of 2.5m above finished floor level.
Just to clarify I'm confused ;) my lights are 2.4m from floor and directly above the pool what Zone am I?
 
Upvote 0
Do you have a current copy of BS7671.
 
  • Like
Reactions: SparkyChick
Upvote 0
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Reading
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Please Help L3 Design Project Selv
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
Mark Wright,
Last reply from
Mark Wright,
Replies
32
Views
5,427

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.