Evening all
I've rad a few posts about running a radial off of a ring and there are loads of different options.
The problem I have is that we have no alternative as the customer already has a spur off the ring and wants a few more sockets but does not want us to start pulling about her kitchen to extend the ring.
so all I can do is change the spur for a FSC and then come off of that..
My question is where do I test up to.
Do I just test up to the FSC or do I test the whole ring.
Thanks for all or any replies:43:
 
if you look at a MWC it asks for details of the modified circuit, not details of the bit you've added. there's your answer.
 
yep, it will be limited to 1 or 2 appliances.
 
Yes but what size appliances??
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Southend on Sea
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Radial off a ring
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Mfctitch,
Last reply from
Pete999,
Replies
4
Views
1,198

Advert