Hi Guys Rcd main switch on board so do you need sup bonding as all circuits are Rcd protected? I know realy need to upgrade board act customer reluctant. Cheers Haj
 
If all circuits in bath/shower room are 30ma rcd protected,required disconnection times are met AND you have a continuity reading of less than 1667 ohms between extraneous conductive parts and conductive parts in the bath/shower room,you dont need supplementary bonding.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

haj

Arms
~
Joined
Location
East Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
I H Electrical

Thread Information

Title
Rcd main switch
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
haj,
Last reply from
Deleted member 9648,
Replies
3
Views
2,677

Advert