I've always overcome this problem by testing the second RCD using the test probes across its load-side line and supply-side neutral. The tester doesn't care whether the test current returns to earth or neutral, it should still perform a valid test on that RCD provided only the line goes through it. But because the test current returns via the the first RCD's neutral, that sees the tester as a legitimate load and shouldn't trip.
Just tried this method and it still trips the RCBO in the main DB
 
Just tried this method and it still trips the RCBO in the main DB
If I understand correctly, it should by L and N to RCD load side as normal, but E probe to the incoming N for that RCD. So no test current in the supply earth.
 
It's hard to see from the picture but does that Earth leakage module not have adjustable settings?
 
I've just googled the part number and it is indeed adjustable, so you can wind its settings up to stop it tripping for the duration of the test.

I'd suggest that, if it is compliant to do so, the trip should be set to something other than 30mA without time delay.
 
  • Like
Reactions: leep82

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

leep82

Arms
~
Joined
Location
Stoke on Trent
Business Name
L.M.P Electrical

Thread Information

Title
RCD's in series and how to test
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
leep82,
Last reply from
davesparks,
Replies
25
Views
7,754

Advert