Only be treated as an aide-mémoire to the Regulations and Electricians should always consult BS-7671:2015: to satisfy compliance.
Appendix 5
Classification of external influences P/400
defined as .
P/28 . External influence . Any influence external to an electrical installation which affects the design and safe operation of that installation.
These external influences are shown by the use of a code which has two capital letters and a number
The first letter shows the category of external influence.
The second letter shows what the external influence relates to and the number indicates the level of the external influence.
The first letter indicates which category the external influence falls under .
A . = Environment - ( wet . dry . vibration )
B . = Utilisation :
• How is the building being used .
• What is the capability of the persons using the building .
• Are they ordinary persons or persons are they handicapped .
C . = Construction of buildings . What is the building constructed from : Non-combustible . Combustible .
The second letter indicates what the external influence could be .
refer to appendix 5 and look in environment section ( category A )
example : if the second letter was K it would refer to; presence of flora ( and/or mould growth )
The last digit is a number and indicates the level of protection which the external influence is likely to be .
External influence given a code of ( AD1)
- Letter (A) relates to the environment .
- Letter (D) relates to water ... AD presence of water .
- Final digit (1) tells you that the problem likely to be caused by water is negligible . ( AD1)
Example: external influence given a code of (AD1)
you can see the letter (A) relates to the environment .
you can see the letter (D) relates to water .
first digit (1) tell you that the problem likely to be caused by water is negligible . (AD1)
you need to look further into Appendix 5 . When you find (AD1) you can see that it relates to areas where weather protection is not required and that the (IP rating ) for the equipment is ( IPX0) As the external influence relates to water nothing is specified for dust (X) and the level of protection against water is (0) which means no protection required .
At the other end of the scale , you can see that (AD8) is where the equipment is likely to be totally submersed, ( such as in a swimming pool )
The ( IP rating ) given as protection is (IPX8) shows that nothing is specified for dust and 8 shows that it must be protection against the effects of continuous immersion in water .
THE INDEX OF PROTECTION CODES IS USED THROUGHOUT BS-7671:2008:2011:2015: to identify the minimum level of protection permissible .
P/405 : A Environment (cont.)
Code External influences : Characteristics required for selection and erection of equipment : Reference for information only .
AD Presence of water
AD1 Negligible
IPX0 Outdoor and non-weather protected locations, with low and high temperatures .
AD2 Free-falling drops
1PX1 or IPX2 Location in which water vapour occasionally condenses as drops or where stream may occasionally be present .
AD3 Sprays
IPX3 Location in which sprayed water forms a continuous film on floor and/or walls .
AD4 Splashes
IPX4 Locations where equipment may be subjected to splashed water; this applies, for example, to certain external luminaires, construction site equipment
AD5 Jets
IPX5 Locations where hose water is used regularly ( yards, car-washing bays )
AD6 Waves
IPX6 Seashore locations such as piers, beaches, quays, etc.
AD7 Immersion
IPX7 Locations which may be flooded and/or where water may be at maximum 150mm above the highest point of equipment, the lowest part of equipment being not more than 1m below the water surface .
AD8 Submersion
IPX8 Locations such as swimming pools where electrical equipment is permanently and totally covered with water under a pressure greater than 0.1 bar .
External influences :
Regulation 301.1. and more particularly Chapter 32 and Appendix 5 of BS-7671: deal with external influences which needs to be assessed by the designer and taken into account in the subsequent installation design and construction .
(ii) The external influences to which it is to be Exposed ( Chapter 32 )
Appendix 5
Classification of external influences P/400
defined as .
P/28 . External influence . Any influence external to an electrical installation which affects the design and safe operation of that installation.
These external influences are shown by the use of a code which has two capital letters and a number
The first letter shows the category of external influence.
The second letter shows what the external influence relates to and the number indicates the level of the external influence.
The first letter indicates which category the external influence falls under .
A . = Environment - ( wet . dry . vibration )
B . = Utilisation :
• How is the building being used .
• What is the capability of the persons using the building .
• Are they ordinary persons or persons are they handicapped .
C . = Construction of buildings . What is the building constructed from : Non-combustible . Combustible .
The second letter indicates what the external influence could be .
refer to appendix 5 and look in environment section ( category A )
example : if the second letter was K it would refer to; presence of flora ( and/or mould growth )
The last digit is a number and indicates the level of protection which the external influence is likely to be .
External influence given a code of ( AD1)
- Letter (A) relates to the environment .
- Letter (D) relates to water ... AD presence of water .
- Final digit (1) tells you that the problem likely to be caused by water is negligible . ( AD1)
Example: external influence given a code of (AD1)
you can see the letter (A) relates to the environment .
you can see the letter (D) relates to water .
first digit (1) tell you that the problem likely to be caused by water is negligible . (AD1)
you need to look further into Appendix 5 . When you find (AD1) you can see that it relates to areas where weather protection is not required and that the (IP rating ) for the equipment is ( IPX0) As the external influence relates to water nothing is specified for dust (X) and the level of protection against water is (0) which means no protection required .
At the other end of the scale , you can see that (AD8) is where the equipment is likely to be totally submersed, ( such as in a swimming pool )
The ( IP rating ) given as protection is (IPX8) shows that nothing is specified for dust and 8 shows that it must be protection against the effects of continuous immersion in water .
THE INDEX OF PROTECTION CODES IS USED THROUGHOUT BS-7671:2008:2011:2015: to identify the minimum level of protection permissible .
P/405 : A Environment (cont.)
Code External influences : Characteristics required for selection and erection of equipment : Reference for information only .
AD Presence of water
AD1 Negligible
IPX0 Outdoor and non-weather protected locations, with low and high temperatures .
AD2 Free-falling drops
1PX1 or IPX2 Location in which water vapour occasionally condenses as drops or where stream may occasionally be present .
AD3 Sprays
IPX3 Location in which sprayed water forms a continuous film on floor and/or walls .
AD4 Splashes
IPX4 Locations where equipment may be subjected to splashed water; this applies, for example, to certain external luminaires, construction site equipment
AD5 Jets
IPX5 Locations where hose water is used regularly ( yards, car-washing bays )
AD6 Waves
IPX6 Seashore locations such as piers, beaches, quays, etc.
AD7 Immersion
IPX7 Locations which may be flooded and/or where water may be at maximum 150mm above the highest point of equipment, the lowest part of equipment being not more than 1m below the water surface .
AD8 Submersion
IPX8 Locations such as swimming pools where electrical equipment is permanently and totally covered with water under a pressure greater than 0.1 bar .
External influences :
Regulation 301.1. and more particularly Chapter 32 and Appendix 5 of BS-7671: deal with external influences which needs to be assessed by the designer and taken into account in the subsequent installation design and construction .
(ii) The external influences to which it is to be Exposed ( Chapter 32 )