I recently tested a doctors surgery and found a number of ring mains
are too large. r1 1.9 rn 1.9 r2 2.7. Zs 1.47 supplied from a type 2 32 amp breaker
could anyone suggest how best to rectify this.
Dont really want involved with the remedials but don't usually refuse work.
any of u guys any suggestions
 
Im sure 1 ring main should not cover more than 100m2 floor area
 
Sorry to point it out again but there's a hell of a difference between 100 metres square and 100 square metres.
Obviously the regs state the former but there does seem to be a lot of confusion over the matter
 
  • Like
Reactions: 5 people
did the test involve visual inspection maybe wire came loose when putting the socket face back on
 
A few computers, printers, a small kitchen
think your right a 20a is the cheapest and easiest way to rectify
 
What is the floor area of this place? I can't imagine it being a massive place. As someone said above, did you check all terminations to make sure they're nipped up nice n tight?
 
It's an old building over 4 floors
basement, ground, 1st, 2nd
havent done the floor area I was just trying to pick some peoples brains
really
 
I think you'll need a slightly more scientific calculation to convince a doctor of your "remedy"!

Not if it's my doctor who just nods and smiles at everything I tell him - which is why six months down the line I am still no nearer to finding out what is wrong with me than I was at the start!!!
 
  • Like
Reactions: 3 people
4 FRC in this building and I estimate the wiring about 30 year old
the circuit has been extended at some time but been done properly
with crimp joints in the back of the sockets
the other ring aims are large aswell
 
Obviously the regs state the former

The only mention of this since the inception of the 17th Edition was that it was a "historical" requirement, and as such no such Regulation still exists!
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring main too big??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
60

Advert

Thread statistics

Created
Boaky,
Last reply from
FAA Greenie,
Replies
60
Views
6,885

Advert