Would you guys be happy with these readings on ring main,Rcbo c type 30ma/32 amp.
r1 1.87...rn 1.91 cpc 3.20....R1 +R2.1.26.
zs 1.46 ohms.
 
some long ring you have there.
[automerge]1573984432[/automerge]
r!+r2 = 5.07 ohms. this equates to approx. 250m, or there's something wrong.
 
Last edited:
Yea,would it comply,Max allowed 0.68 ohms,but......
 
As long as there is no volt drop concerns for the circuit and the rcbo when tested gives adequate earth fault protection, then it is what it is.
 
  • Agree
Reactions: westward10
Is it actually that long ? Those would be the highest readings I've ever seen for such a circuit.
 
What size cable is it?....and why a “c” type?....I have no answer to your question but am genuinely interested ?
 
2.5 mm lsoh t&e,measurement correct,it’s along one,also did short circuit measurement,according to my cals it does not comply.
 
Is it actually that long ? Those would be the highest readings I've ever seen for such a circuit.
scary ain’t it.
 
It is quite a long circuit, but from the fact that it is a C32 RCBO, I'm suspecting this is commercial / industrial, rather than domestic? For example, a ring in a large workshop, warehouse, school, etc.

I'd be wondering about the voltage drop, e.g. are all the loads at middle of the ring because the outlets happen to be a long way from the distribution board?

Or has someone used a somewhat too small cable size, e.g. 1.5mm2 T&E or SWA?
 
It’s in a quite a large office area,it’s defo 2.5mm,difficult to judge where the actual loads are,there are mainly,computers plugged in.Been in service @ least 5 years,all signed of.
 
It’s in a quite a large office area,it’s defo 2.5mm,difficult to judge where the actual loads are,there are mainly,computers plugged in.Been in service @ least 5 years,all signed of.
That sounds like most of my customers.....worked fine like that for years ?
 
It’s in a quite a large office area,it’s defo 2.5mm,difficult to judge where the actual loads are,there are mainly,computers plugged in.Been in service @ least 5 years,all signed of.
if that's the case, why not replace MCB with a B type, even drop to a 20A?
 
  • Like
Reactions: Baddegg
T9
if that's the case, why not replace MCB with a B type, even drop to a 20A?
true that could be done,note on recommendations.
Even rcbo @ 20 amp
 
Sorry to hijack the post but for someone still learning how do you work out the length of circuit from the readings ie what would the formula be please ? Tia
 
Sorry to hijack the post but for someone still learning how do you work out the length of circuit from the readings ie what would the formula be please ? Tia
Look in the on-site guide, appendix, I think it's table 11

It gives the R1+R2 resistance per metre

So for 2.5/1.5 it's around 19.5 miliohm per metre if you know the length, it's length x this value, if you know the overall resistance it's the resistance devided by the resistance per metre

You could also work it out from R1 for 2.5mm2 per metre, plus R2 for 1.5mm2 per metre

These values are also in the table
 
  • Like
Reactions: Baddegg
For a ring final, use an end-to-end reading, eg. the line conductor r1.

Length of conductor = resistance of conductor ÷ resistance of conductor per meter

For a 2.5mm² conductor, resistance per meter is 7.41mΩ, or 0.00741Ω. So:

Length of conductor = r1 ÷ 0.00741
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Eicr ring main readings
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
cliffed,
Last reply from
Gary latto,
Replies
19
Views
3,903

Advert