I know the subject of transporting pme from a house to an out building has been discussed many times.
This question is the DNO is only providing a single phase no earth TT supply which is fine. Want to run a sub main with swa to an out building approx 30m away. Would you only connect the the armour supply side (at the house) and only use a plastic gland outbuilding side or would you use an swa gland both ends and fit earth rods at both buildings all linked together or rods at both buildings but the earths are not connected between the two. This is small holding no other properties nearby.
 
as above. rod and earth both ends, better still is add a rod or 3 more, 1 at each end > 1m from existing .
 
Any additional rods should be outside the zone of influence of the closest rod, this means at least the length of the existing rod away from any other.
 
Any additional rods should be outside the zone of influence of the closest rod, this means at least the length of the existing rod away from any other.

Is this correct or should they be spaced by the the combined length of both rods?
 
You could be right, I will have to look it up again, for some reason 2.2 times rings a bell.
 
Any additional rods should be outside the zone of influence of the closest rod, this means at least the length of the existing rod away from any other.
Three times the length of the original rod to ensure you're outside the sphere of influence. There is a calculation for this but this is a good rule of thumb.
 
  • Like
Reactions: nicebutdim
Last edited:
  • Like
Reactions: Strima
  • Like
Reactions: Soi disant
Geophagy has been considered as an adaptive behavior in humans and animals (1) and the clays have been considered the healing materials from ancient times. As geophagia is an occasionally habits of animals and humans (babies and pregnant women), physiologically it is assumed that earth might have some beneficial effects on body function. Bentonite is absorbent aluminium phyllosilicate clay. It is named after Fort Benton, Wyoming where its largest sources are found.
 
All true, I missed that point, obviously thought the post was referring to Bentonite not being a natural clay.
 
  • Funny
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Transporting TT earthing?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
14

Thread Tags

Tags Tags
earthing

Advert

Thread statistics

Created
mjf,
Last reply from
Mike Johnson,
Replies
14
Views
3,019

Advert