Search the forum,

Discuss True or False..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Guest123

So, got a call this morning from local authority saying that a number of houses on a site we had worked on had "lost" power. Ok says I, I'll shoot straight over, no worries.:cool:


Turns up to about 17 ressies all standing on their doorsteps with pitchforks and torches in hand, waiting for me as it turns out.:(

What's up says I......come and smell my telly says one of them!!!!:confused::confused:

To cut a long story short, it turns out that no less than 18 television sets had totally burned out....due to a SUPPLIERS problem, felt the relief I did.:rolleyes::D

So I'm chatting to the DNO guys assuming there was a surge of some kind on that particular line. no no says the chap.....we lost a neutral.

Lost a neutral......are you sure??? definately he says.

Now it may be me but would a loss of suppliers neutral really cause 18 T.V's to flombay themselves.....opinions please gents.:)
 
could be overvoltage or undervoltage - DSO lost the 'star'(neutral) point on the 3-phase trafo
 
Last edited by a moderator:
Hi,
Definately true as we lost the main neutral at work and it resulted in every piece of equipment one of the phases smoking.

The way I visualise it is to imagine equal single phase loads on a 3 phase board.
If the neutral to the board was lost then equipment will still operate due to a return path through another load on a different phase as they are joined by the neutral rail.
The equal loads will mean that the voltage across each load will remain the same.
If the loads were not equal then you will get voltage rise on one load and voltage drop on the other.

If you had 2 resistors of equal value in series across a 24 v supply you will measure 12v across each resistor.
If the resistor values were different then the voltage across each resistor will also be different.
 
Clutching at straws here perhaps but, maybe someone from the suppliers cross conneted an outgoing phase with a neutral on an item of switchgear or a cable joint that resulted in a 2 phase supply instead of phase- neutral

Why only televisions though ?

I thought BT were the biggest culprits for frying electronic equipment, with lightning strikes on their phone lines, when questiioned they say " Not us GuV"
 
It may have taken out the TV's but other appliances could have been damaged but have not failed yet.

About 10 years ago got called to an intruder alarm fault in a hospital it was quite a big system with multiple power supplies most had failed as the sub station earthing / neutral had failed and the resulting floating neutral caused one phase to have 300+ volts on it
 
There is a post somewhere in the Chit Chat off topic section and fairly recent regarding something similar.
Some halfwit pikey broke into a substation and nicked the neutral link to weigh in for scrap, fried god knows how many consumer units. Have a look in there it make scary if not interesting reading.

Cheers........Howard
 
ya -if you disconnect the neutral on a 3-phase board feeding SP loads

you're left with an unbalanced star connected 3-phase load

voltages will vary up/down from the nominal 230V
 
Done a bit of digging on this today, to try and find out exactly what went on.

Having spoken to a couple of guys from the DNO who were honest and weren't lying to try and save face, turns out that the connection at the star point of the trafo was lost, sending upto 400V AC down the "floating" neutral conductor. Basically a massive over-voltage situation causing thousands of pounds worth of damage to T.V's, heating boilers, showers, pir lights etc etc.


I suggested this situation to the chaps form the DNO who were on site yesterday and they swore blind it wasn't the case.....lying toerags!!! It seems they have now admitted liability and are going to pay up for all the repairs.
 
Three phase with lost neutral will give up to line voltage on one phase and down to zero on another. With single phase ie disconnected neutral at origin you will still get damage to electronic equipment especially with florescents trying to strike as the back EMF will try to find a way through the filter circuits in electronic devices back to earth.
 
ive had this happen lost neutral in a hotel , blew every HF ballast and emergency light in the building cost a fortune to replace and two weeks after the same thing again but this time blew up 2 single phase pumps which cost a fortune to get rewound , cant remember what supply it was but i think it was tncs , as i was getting reports of people getting shocks off the metal work in the building
 
Seemples. Imagine a number of houses connected to three phase supply cable. Each house is in rotation connected to one phase and neutral. Each house's supply flows in through the phase conductor and out through the neutral conductor. If at some point the neutral conductor is broken, the return voltage from one house can travel via the neutral conductor to the next house. That voltage meets another phase at the customer's equipment. Smell of burning. TVs, microwaves etc. damaged. Word goes around, and before you know it, half a dozen 32" CRT TVs have turned into a hundred 50" plasmas. QED. If it's a PME supply, and if the neutrals have been earthed at every joint as required, damage is much less likely. Similarly, if the supply cable is a ring, damage is avoided. It's where neither of these conditions is satisfied that the trouble starts.
 
Last edited by a moderator:

Reply to True or False..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock