Doesn't this current leak through either the main earth or the bonding conductors?

In an ideal world it would yes, but in reality some will flow elsewhere too. Parallel paths, fortuitous connections to earth or even the fault you are trying to find could be diverting the leakage current elsewhere.
 
In an ideal world it would yes, but in reality some will flow elsewhere too. Parallel paths, fortuitous connections to earth or even the fault you are trying to find could be diverting the leakage current elsewhere.

I imagine the easiest way of imagining it is a bonding conductor connected to a pipe for example, is just a potential divider.
 
When you say clamp around all live conductors at once do you mean both the supply live and neutral? If so, why will this reading be different to clamping the main earth and bonding conductors?
Both live conductors will have magnetic influence on each other due to current draw but these are cancelled out by each other. If there's some leakage going a different route there will be a part of the magnetic field that isn't cancelled out giving you a reading.

I tend to test with all conductors clamped, both lives and earth, then just the live conductors. This gives a ball park figure of what is finding parallel paths and what is going back down the main earth conductor.
 
I would clamp around the L-N of the outgoing problem RCD.
I tried to say this earlier in the thread but after re-reading my previous doesn't make much sense.
 

Reply to Understanding what this means on the megger 1731 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
290
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I've just been to a job to replace a burned out switch where the customer supplied his own Arlec dimmer switch. During a dull moment, I read the...
Replies
6
Views
712
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
354
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock