Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms.
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
 
Sounds like the earth has shorted on the beginning run of the cable as you had 0.35 on rn/r1 must be the earth ring is so short it reads 0.00 does your tester go to three figures? Have you tested at the middle socket? r2? end to end that would indicate if that was the case.
 
Back there Friday to finish up so I'll check more extensively then, closest socket to board 0.09 ohms which is very close to the board. Is a really small ring too. Cheers
Tested R1 +R2, and R1 to RN too etc to check all. Yes tester goes to 3 figures is Fluke 1653B
 
Cpcs aren't jointed together in the board? Try testing at a socket.
 
  • Like
Reactions: Specialist
Something on the ring has a parallel earth paths? How water heater etc..
 
Was testing at sockets with kewtech plug adaptor but wondering if the two croc clips I was using not connecting tight at board or similar.
 
Well if you get zero ohms that is good contact.
 
What position are you testing the ring from the consumer unit or socket ? I have had it in the past where had small ring and the dampness of plaster damp wall between the metal k.o. boxes have given a lower continuity reading than I should of had but not that low.
 
  • Like
Reactions: Specialist
What position are you testing the ring from the consumer unit or socket ? I have had it in the past where had small ring and the dampness of plaster damp wall between the metal k.o. boxes have given a lower continuity reading than I should of had but not that low.
Tested at each socket on newly rewired small ring, as said expected around 0.58 and got 0.00! After 0.35 each on L's & N's cross connected.
 
Maybe cables have been jointed somewhere but cpcs have been connected together in one connection rather than connected in 2 separate connections.
But 0.00 ohms suggests that the cpc ends are crossed in the db with another circuit
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Soulsurfer

Arms
~
Joined
Location
Channel Islands
Business Name
M.B.S ELECTRICAL

Thread Information

Title
Renovated house low r2 readings !
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
64

Advert

Thread statistics

Created
Soulsurfer,
Last reply from
HandySparks,
Replies
64
Views
7,011

Advert