Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a ring final circuit which does the rest of the house apart from the kitchen.

R1 and R2 all ok etc, loop test fine but doing the insulation resistance shows nearly a dead short L-E and N-E but if you reduce the test voltage to 250V its showing about 100 meg. The upstairs rooms are absolutely full of junk and furniture and a few sockets look to be DIY fitted, extension cables under carpets, that sort of thing so no way of finding the fault without emptying the room and the company is only getting paid to put the sockets back the way they were.

Firstly what do people do when they come across stuff like this, if you insist on the house being emptied the insurance company will just use another firm that isn't as picky and the insurance money the contractor gets is good enough to buy him a new electric Porsche so that is definitely not going to happen, and the guy with the Porsche gives us loads and loads of excellent work so we aren't going to be awkward either.

Secondly I didn't think of this until I'd left, is it possible the fault is caused by a surge protection extension lead plugged in somewhere, I've had it in the past where it mimics a short to earth but once unplugged the readings are fine. If there was a real fault there is would show up on the 230V setting as well wouldn't it.
 
I occasionally come across a fault that shows at 500V but not at 250V. Rare, but not unheard of. Last time was due a cable that had been slightly nicked by a socket screw.

If it was a surge protection extension lead, I would expect a steady reading of ~0.4 Mohms at 500V, give or take.

What would I do? As long as I was sure that it's not a fault that I had caused, I would inform the person ordering the work in writing that there is an existing fault that needs further investigation.
 
I occasionally come across a fault that shows at 500V but not at 250V. Rare, but not unheard of. Last time was due a cable that had been slightly nicked by a socket screw.

If it was a surge protection extension lead, I would expect a steady reading of ~0.4 Mohms at 500V, give or take.

What would I do? As long as I was sure that it's not a fault that I had caused, I would inform the person ordering the work in writing that there is an existing fault that needs further investigation.
Yea it wasn't a dead short and was more than 20k on the low ohm setting, cant remember the reading but it was somewhere around what I've seen before with those surge protection leads, I just didn't put two and two together before I left. Its just that I have never tried meggering a surge lead with 250V before to see what it reads so was a bit confused that it passed with the 250V setting. The only reason it was on the 250 setting was I tried it across the L&N to see if anything was still plugged in but not frying a PC or something and forgetting to turn it back to 500.
 
Seeing < 1M on 500V but > 10M on 250V is the classic result of SPD. It could be something else of course, but seeing much the same on both L-E and N-E (if L-N largely open) really points to that.

It is probably a protected 13A block plugged in somewhere for IT stuff or TV, but occasionally you see it built in to equipment like a boiler, etc.
 

Reply to Low insulation reading at 500V in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725
I recently fitted a Heatmiser Neostat for a customer in their hall- to control their radiators throughout the house (70’s 4 bed medium sized...
Replies
3
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock