Yes providing the armour is effectively earthed. Additional rcd protection is not required and an s type 100ma rcd does not provide additional protection anyway.
Reactions: Ian1981
PME
So would you happy to run say a 16mm 3C swa from a 63a isolator to the consumer unit? No need for any RCD on the supply and above a ceiling/under the floor?
Why are you making reference to floors,ceilings and Rcd when considering swa
Why would it need that? Nothing in BS7671 about it, and the DNO may not specify it.
No, but as you know it's a common and well-known requirement.
Hi - please confirm suppliers fuse, installation load, Ze, cable distance and installation method etc. Otherwise they're all going to argue pointlessly :) .
Reactions: EbolaSideRoom
My understanding is that the DNO will not generally allow their fuse to be used to protect any part of a consumer’s installation.
The 3m stipulation relates to the BS7671 requirement that overload protection must be provided within 3m of a reduction in the CCC of a conductor.
Where can I find this 3m rule in BS7671?
Submain Supply 100a 100mA
Tom Christopher,
Zdb,