Hey all
I am a 17th edition sparky... but currently not actually doing much electrical work.
I work with a CCTV company that basically do as they please when it comes to regs, doing a job properly etc.
They have asked me to go test all the emergency lighting in a public building, and I wondered what certs etc should be issued in regards to this.
I am competent, but basically after checking them all and identifying what needs replacing, new batteries etc.... are we supposed to issue a cert or something? I have never in my 38 years of sparking been that involved with emergency lighting.
Are we supposed to identify what lights have no test switch etc?
Personally, I would rather they get a local sparky in.... but that just isn't gonna happen.
Any guidance gratefully received!
 
Has your company provided you with a copy of BS5266:1 2016.
 
we use equipment tags and test monthly the tags have a comment section on them and we were required to list what was changed or repaired and the date. also the info needed to be entered in the facility engineers logbook.
the local fire marshal audits these books 4 times a year.
but the regs in your country are different than ours
 
If not a "cert" as such you could enter your findings into a spreadsheet and email it to the person ordering the work.
 
If not a "cert" as such you could enter your findings into a spreadsheet and email it to the person ordering the work.

exactly if there is not a cert form for it you have proof that it was done as long as you retain a copy and have sent it to all the pertinent people involved
 
If you are testing emergency lighting systems then you should be competent and understand the implications of BS5266: Part 1.

There should be a log book for the system(s) and you would be signing this log book to confirm that the installation is, and continues to be, compliant with the various requirments.

If you don't know about this, then don't do it. If there's a fire and the occupants of this public building cannot get out because your "certified" emergency lights don't work, then it will be YOUR dangly bits on the chopping block when the courts come to pin the blame on somebody.

Just saying.....
 
What test is this annual or quarterly? Have you examined existing log books if any? What type of system is it? How many are there. Does the design comply in the first place?
 
  • Optimistic
Reactions: 1 person
The only tests recommended are monthly and annually. Annex K of BS5266:1 suggests a Certificate to be used for the verification of existing installations, we use something based on this format. Annex M shows a Model periodic inspection and test certificate.
Signing a log book to say you have tested it does not assume the system is adequate or compliant, the log book is only the history of the system which should also include all other works carried out to it. If you feel the system is inadequate or non compliant you state this in the log book and ensure the responsible person/s are forwarded copies of the certificates. EN 50172 gives details of log book requirements.
 
Hmm
As far as I am aware, there are no previous records of testing.
I wondered if I am supposed to purely test the condition of the fittings and batteries, or actually indulge in whether they are correctly placed, have test switches, adequately light the area etc

Oh... I forgot my password and tried to request a new one on here.... the Capatcha anti-spam request for a new password is totally impossible on this website. Lucky I finally remembered the original password.
 
Has your boss provided you with the correct information to undertake this task.
 
Nope. He sent an untrained guy there who refused to do it. So, seeing as I am 17th qualified, I now have been lumbered with the task. Doesn't make me any happier about it... hence the questions.
I just don't know exactly what I am supposed to check and note
 
I suggest you refuse to do it too. 17th edition and BS7671 has nothing to do with emergency lighting.
You aren’t competent in this particular area.
 
As a 17th edition Electrician, you can conduct a periodic inspection of the wiring and equipment.
You can state whether the system is electrically safe for continued use.
You would not necessarily be able to state whether the system complies with BS5266-1.
 
  • Agree
Reactions: telectrix
Thanks. I am competent. I just was not 100% sure of the implications and requirements.
I will take a look Monday and make an informed judgement.
 
I don't have a copy of BS5266 and I'm not about to fork out £122 for one, but I'd like to think I'm competent to turn a switch off and on again once a month, and I'm even willing to initial to say I've done it.

The way I see it emergency light testing is like fire alarm testing or even PAT testing (ISI&TEE) - you're not designing a system, just testing it, and a caretaker could do that.

Again, I haven't done a special course and got a certificate to say I can design an emergency lighting system, but I can integrate emergency lighting into the primary lighting system, and in a situation where nobody else is going to consider emergency lighting until it's too late I'd be happy to put my neck on the line. Same with the testing of it - I'm happy to take that on if nobody else will.
 
Thanks. I am competent. I just was not 100% sure of the implications and requirements.
I will take a look Monday and make an informed judgement.
Being competent I assume you have a good working knowledge of the necessary standards and requirements.
 
I don't have a copy of BS5266 and I'm not about to fork out £122 for one, but I'd like to think I'm competent to turn a switch off and on again once a month, and I'm even willing to initial to say I've done it.

The way I see it emergency light testing is like fire alarm testing or even PAT testing (ISI&TEE) - you're not designing a system, just testing it, and a caretaker could do that.

Again, I haven't done a special course and got a certificate to say I can design an emergency lighting system, but I can integrate emergency lighting into the primary lighting system, and in a situation where nobody else is going to consider emergency lighting until it's too late I'd be happy to put my neck on the line. Same with the testing of it - I'm happy to take that on if nobody else will.
When you integrate emergency lighting into an existing system how do you go about this, what are your primary considerations.
 
  • Optimistic
Reactions: 1 person
When you integrate emergency lighting into an existing system how do you go about this, what are your primary considerations.
Generally the same considerations as for the primary lighting system, such as the use of the space and future maintenance, plus the direction of the escape route.
 
  • Funny
Reactions: 1 person
What photometric data do you provide, see BS5266:1 2016.
 
  • Optimistic
Reactions: 1 person
I don't have a copy of BS5266 and I'm not about to fork out £122 for one, but I'd like to think I'm competent to turn a switch off and on again once a month, and I'm even willing to initial to say I've done it.

The way I see it emergency light testing is like fire alarm testing or even PAT testing (ISI&TEE) - you're not designing a system, just testing it, and a caretaker could do that.

Again, I haven't done a special course and got a certificate to say I can design an emergency lighting system, but I can integrate emergency lighting into the primary lighting system, and in a situation where nobody else is going to consider emergency lighting until it's too late I'd be happy to put my neck on the line. Same with the testing of it - I'm happy to take that on if nobody else will.
Hi Adam w,

I've feel I must disagree. I have no quals in emergency lighting also, but suspect I may be able to test correctly,

But the reason I wouldn't do this job (just because I suspect I could do it )is I don't know what I don't know.

there are parts of this job I may be ignorant of so it would be unfair and wrong to charge a customer for works I am not compitant in doing.

Thinking your compitant or suspecting your compitant does not make you compitant.

If I where to take on a job such as this I would at the very least get a copy of bs5266 and go on a course.
 
Its an awkward one as i have worked in several buildings where the emergency lighting is checked monthly in house by designated office staff, who were not say competant to design a system but they could flick a key switch and see if they lit or not. Im sure if you had in writing that you are literally carrying out functional or a 3hr test only and that if compliance of that system with bs5266 needs to be confirmed then somebody competant to do so should be appointed if so required?

I don't see how that leaves you open to any liability as your only doing as asked and have made clear that that task doesnt nescacerily (sp?) mean it complies with relevant regs?
 
  • Agree
Reactions: 1 person
In my experience, the monthly functional test can be carried out by the cleaner, who ticks off a log sheet.
But
Initial certification and the required 12-monthly soak/discharge checks must be done by someone who knows the requirements.
Passing the “17th Edition” does not make you competent wrt Em Lighting.
 
Thanks. I am competent. I just was not 100% sure of the implications and requirements.
I will take a look Monday and make an informed judgement.

here is where your code books come into play, different designs and setups can preset different requirements and amendments to code and are generally detailed in the code books.
when i had to inspect at work I carried a copy of the specific pages of the code book right with the clip board (even though i had them memorized).
our company would do the initial inspection with 1 inspector ( a master) and 2 witnesses (usually a journeyman and an apprentice)
subsequent inspections were done by the qualified journeyman and apprentice to verify the system continues to operate and hasn't been altered in any way. Proper documentation was required and the company was fined if it wasn't done correctly.

as others have stated if you are unsure you shouldn't do the inspection or at least have a copy of the pertinent regs to refer to.
 
If you are testing emergency lighting systems then you should be competent and understand the implications of BS5266: Part 1.

There should be a log book for the system(s) and you would be signing this log book to confirm that the installation is, and continues to be, compliant with the various requirments.

If you don't know about this, then don't do it. If there's a fire and the occupants of this public building cannot get out because your "certified" emergency lights don't work, then it will be YOUR dangly bits on the chopping block when the courts come to pin the blame on somebody.

Just saying.....

You sign the logbook to say you have inspected. Not that it is compliant.
 
I don't have a copy of BS5266 and I'm not about to fork out £122 for one, but I'd like to think I'm competent to turn a switch off and on again once a month, and I'm even willing to initial to say I've done it.

The way I see it emergency light testing is like fire alarm testing or even PAT testing (ISI&TEE) - you're not designing a system, just testing it, and a caretaker could do that.

Again, I haven't done a special course and got a certificate to say I can design an emergency lighting system, but I can integrate emergency lighting into the primary lighting system, and in a situation where nobody else is going to consider emergency lighting until it's too late I'd be happy to put my neck on the line. Same with the testing of it - I'm happy to take that on if nobody else will.

Everything wrong with our industry in a single post right here.
 
Any competent Electrician can install, test and maintain an emergency lighting system.
It takes a bit more info to design or to state whether an existing system complies.

Part of the testing is to verify an existing design is in place and that it is current.
 
Part of the testing is to verify an existing design is in place and that it is current.
Sorry, that would be initial verification.
Monthly or annual testing, battery duration testing and functional testing do not require verification of design.
Any alterations which could affect the existing design, such as new walls, different colour scheme, etc, should result in a revised design at the time of the alteration.
 
I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
 
  • Agree
Reactions: 1 person
Monthly or annual testing, battery duration testing and functional testing do not require verification of design.

Annex K of BS5266:1 provides a Certificate for this exact purpose.
 
I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
In many instances, the installer is installing to a design supplied by another.
Cables is cables whether it’s for power and lighting, emergency lighting or fire alarms.
Such installers don’t need to know the maximum height of a void above a ceiling before a smoke head has to be installed.
They don’t need to know whether the head should be heat or ionisation.
They don’t need to know the minimum distance from a wall, or from light fittings and other equipment.
They don’t need to know when an emergency exit sign should be maintained or non-maintained.

Yes knowing such things would be useful, but as long as they install as per the design, everything should be ticketyboo.
 
In many instances, the installer is installing to a design supplied by another.
Cables is cables whether it’s for power and lighting, emergency lighting or fire alarms.
Such installers don’t need to know the maximum height of a void above a ceiling before a smoke head has to be installed.
They don’t need to know whether the head should be heat or ionisation.
They don’t need to know the minimum distance from a wall, or from light fittings and other equipment.
They don’t need to know when an emergency exit sign should be maintained or non-maintained.

Yes knowing such things would be useful, but as long as they install as per the design, everything should be ticketyboo.
That may be the case but this does not change the fact a multitude of systems are not compliant. Assessing whether AFDs are required in voids can only be known if the Category of system is known. Minimum spacing from walls and luminaires is a basic requirement for any Category of system.
 
  • Agree
Reactions: 1 person
I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
Perhaps, as you seem to be suggesting, nobody considered themselves sufficiently competent to upgrade it, so just left it alone.
 
If you are annual or monthly testing you do not need to verify the design. Comments should be noted on test certificate & log book. If the fire risk assesment deems it an unsatisfactory design then that will force the client to take action.
Annual test you are there to test that the battery withstands the 3hr test without the light fading. No new exits or walls are apparant and the general el install, i would always comment if no easily accesible key switch is readily available but wouldnt give an unsatisfactory if there wasnt one.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Testing emergency lighting
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
63

Advert

Thread statistics

Created
Steve2381,
Last reply from
Adam W,
Replies
63
Views
12,384

Advert