- Jul 15, 2016
- 23,299
- 1
- 29,151
- 315,788
- United Kingdom
- Electrical Engineer (Qualified)
See posts #16 and #20.What photometric data do you provide, see BS5266:1 2016.
Hi Adam w,I don't have a copy of BS5266 and I'm not about to fork out £122 for one, but I'd like to think I'm competent to turn a switch off and on again once a month, and I'm even willing to initial to say I've done it.
The way I see it emergency light testing is like fire alarm testing or even PAT testing (ISI&TEE) - you're not designing a system, just testing it, and a caretaker could do that.
Again, I haven't done a special course and got a certificate to say I can design an emergency lighting system, but I can integrate emergency lighting into the primary lighting system, and in a situation where nobody else is going to consider emergency lighting until it's too late I'd be happy to put my neck on the line. Same with the testing of it - I'm happy to take that on if nobody else will.
Thanks. I am competent. I just was not 100% sure of the implications and requirements.
I will take a look Monday and make an informed judgement.
If you are testing emergency lighting systems then you should be competent and understand the implications of BS5266: Part 1.
There should be a log book for the system(s) and you would be signing this log book to confirm that the installation is, and continues to be, compliant with the various requirments.
If you don't know about this, then don't do it. If there's a fire and the occupants of this public building cannot get out because your "certified" emergency lights don't work, then it will be YOUR dangly bits on the chopping block when the courts come to pin the blame on somebody.
Just saying.....
I suggest you refuse to do it too. 17th edition and BS7671 has nothing to do with emergency lighting.
You aren’t competent in this particular area.
Any competent Electrician can install, test and maintain an emergency lighting system.
It takes a bit more info to design or to state whether an existing system complies.
You flick a switch and see if the lights come on. It isn't rocket science.Everything wrong with our industry in a single post right here.
Sorry, that would be initial verification.Part of the testing is to verify an existing design is in place and that it is current.
In many instances, the installer is installing to a design supplied by another.I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
That may be the case but this does not change the fact a multitude of systems are not compliant. Assessing whether AFDs are required in voids can only be known if the Category of system is known. Minimum spacing from walls and luminaires is a basic requirement for any Category of system.In many instances, the installer is installing to a design supplied by another.
Cables is cables whether it’s for power and lighting, emergency lighting or fire alarms.
Such installers don’t need to know the maximum height of a void above a ceiling before a smoke head has to be installed.
They don’t need to know whether the head should be heat or ionisation.
They don’t need to know the minimum distance from a wall, or from light fittings and other equipment.
They don’t need to know when an emergency exit sign should be maintained or non-maintained.
Yes knowing such things would be useful, but as long as they install as per the design, everything should be ticketyboo.
Perhaps, as you seem to be suggesting, nobody considered themselves sufficiently competent to upgrade it, so just left it alone.I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.