If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Might be trivial question. My understanding is that we test on either leg of the ring since both legs make up a radial, but some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test, but I don't see why not if the other leg is "wago-ed".
 
if you disconnect both L and N from DB, all you have then is 1 long radial.testing either end of L or N to E will give you your IR readings. you can test L-N as long as nothing is connected.
 
  • Like
Reactions: static zap and mak
If you have ring continuity it makes no difference. But wise to check r1 / rn / r2 first so you know you are testing all socket in the ring and noy just those up to a break.
 
some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test.

It is not a live test, it is a dead test. The IR test is performed with the circuit isolated (dead).

As long as you have proved ring continuity before doing the IR test then it does not matter if you connect to one L or both etc
 
  • Like
Reactions: static zap
It is not a live test, it is a dead test. The IR test is performed with the circuit isolated (dead).
I know it's a test done on an deenergized board/circuit but you still send 500V through the circuit so it's kind of live.
 
I know it's a test done on an deenergized board/circuit but you still send 500V through the circuit so it's kind of live.
IT'S a dead test Mate, voltage is applied not sent through
 
IT'S a dead test Mate, voltage is applied not sent through
Sorry mate, I'm not a linguistics engineer, what's the principal difference between "sending" and "applying" in this context.
 
  • Like
Reactions: electric al
Sorry mate, I'm not a linguistics engineer, what's the principal difference between "sending" and "applying" in this context.
Volts don't flow. are not sent anywhere, they are a pressure that is applied to a circuit to put it in Layman's terms.
 
Volts don't flow. are not sent anywhere, they are a pressure that is applied to a circuit to put it in Layman's terms.
So you virtually can't get a shock from it?
 
So you virtually can't get a shock from it?
What makes you think you wont get a belt from an insulation tester probably set at 500V dc, put it another way don't grab hold of the IR test leads when Applying the voltage.

Did you not cover Potential Difference and Current flow during your training?

Being a dead test means the the supply to the circuit is isolated, switched OFF, as you would in any dead test, never had the pleasure of some Sparky telling you to " hang on to these leads a second Mate please and pressing the test button, or in my Apprentice days winding the handle on an IR tester?

No I guess not. Makes yer eyes water a bit, and wakes you up, frowned upon these days though,
 
Last edited:
What makes you think you wont get a belt from an insulation tester probably set at 500V dc, put it another way don't grab hold of the IR test leads when Applying the voltage, did you not cover Potential Difference and Current flow during your training?
Maybe I did or maybe the training these days is rubbish. I guess my question is how big is the current while performing the test, if it's not considered to be a live test then the current must be very little...
 
Maybe I did or maybe the training these days is rubbish. I guess my question is how big is the current while performing the test, if it's not considered to be a live test then the current must be very little...
Enough to make you jump and drop things.
[automerge]1596717083[/automerge]
 
  • Like
Reactions: mak
It's a dead test because the circuit being tested is not energised when the tester is connected. Yes, the yesterday itself puts a voltage across the conductors, but the system does not.
 
This may help you understandhttp://www.-----------.co.uk/Inspection-and-Testing-Insulation-Resistance-Test.php
As may this site
 
It's a dead test because the circuit being tested is not energised when the tester is connected. Yes, the yesterday itself puts a voltage across the conductors, but the system does not.
Yesterday.....is that what you've christened your IR tester?
 
Yesterday.....is that what you've christened your IR tester?

Blinking flip! And it's too late to edit it now.
 
  • Funny
Reactions: HappyHippyDad
Blinking flip! And it's too late to edit it now.
Don't worry, it seems IR dead testing is all in the past anyway.....;)
 
  • Funny
Reactions: DPG
Maybe I did or maybe the training these days is rubbish. I guess my question is how big is the current while performing the test, if it's not considered to be a live test then the current must be very little...
Yes that's plain to see.
 
500v/1MΩ minimum how many amps is that?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

mak

~
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Insulation resistance test on a ring final circuit
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
mak,
Last reply from
ipf,
Replies
30
Views
14,598

Advert