Hi guys
I’ve been requested to replace a consumer unit but will need relocating lower within a tight cupboard.
I will be installing a box with din rail and terminals etc and running new cables to new unit.
Problem I have is that the meter and isolator is mounted on a board. The only way to reposition the board to acceptable location is to run cables behind board.
I know it’s not great practice but no other possible route. Just wondered what your opinions are.
Cheers guys.
 
Does it really need relocating.
 
  • Agree
Reactions: 7029 dave
The outgoing final circuits from the new consumer unit will almost certainly be RCD protected so having them 'buried' isn't really an issue. I'm assuming safe zones are created by the new CU or your joint box?
The only real issue is extending and running the incoming supply. What cable are you running the supply in? If T+E could you put a plate on front of the board so the supply is mechanically protected?

EDIT - read it again now and realise you aren't moving it very far so will probably be tails from isolator straight in.
 
I know work is work, but I dont see the value add to this task.
 
I know work is work, but I dont see the value add to this task.
Hopefully the OP will clarify the actual purpose.
Only two logical reasons are coming to me - It might be that an old Wylex needs changing and there isn't room in original location.
Or it might be that the original position is not able to be reached by an elderly customer.
 
  • Like
Reactions: 7029 dave
Does it really need relocating.
Unfortunately yes. It’s not far from the ceiling and the ceiling is sloped. It’s a struggle to take the cover from the existing
 
So how far are you moving it that the circuits need extending.
 
So how far are you moving it that the circuits need extending.
About a meter lower. All the existing cables enter the rear of unit.
 
Hopefully the OP will clarify the actual purpose.
Only two logical reasons are coming to me - It might be that an old Wylex needs changing and there isn't room in original location.
Or it might be that the original position is not able to be reached by an elderly customer.
It is an old wylex with limited space and also the customer is old and can’t access where it is. You were right on both counts!!! Lol!!!
 
  • Like
Reactions: timhoward
I know work is work, but I dont see the value add to this task.
No room for a modern unit where the existing old wylex is now. Has to be moved. Also more accessible for elderly customer
 
7F92A6DF-B6B6-40B0-8D8B-BCCC7C05BE12.jpeg
E423C00D-9298-4C35-AFDC-D4F3BA4B853B.jpeg
 
Running them behind the board is fine. DIN rail or push fit connectors in an enclosure is also fine.
 
Running them behind the board is fine. DIN rail or push fit connectors in an enclosure is also fine.
Ok great. Thanks for all your replies 👍
 
  • Like
Reactions: timhoward and DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
South Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Relocation of consumer unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Kopboy,
Last reply from
Kopboy,
Replies
12
Views
2,714

Advert