I suspect the problem is caused by the ssr becoming too hot and its internal thermostat acting to shut off the relay. I have a query with sensata/crydom to confirm as I suspect their latest next generation* D2425 SSRs contain an electronic thermostat to protect its electronics. Certainly the D2425 specification says the maximum ambient temperature is 80C, and at this temperature and above the current it can handle must be reduced ie the device de-rated from 25A. And the reference below describes an internal thermostat within the SSR package.

* The previous SSR was an earlier generation I reckon without a thermostat. Note the original SSR was assembled in Mexico whereas the new one does not mention where it was assembled.

https://www.sensata.com/sites/defau...tection-for-solid-state-relays_whitepaper.pdf

At the moment there are two problems with the way the SSR is installed. The first is the fins are horizontal - they should be vertical to maximise cooling by convection flow of air over the heat sink. The second it appears the SSR and heatsink is within a sealed enclosure adjacent to the very hot oven chamber. The SSR even with a heatsink properly orientated will have great difficulty keeping cool enough inside this enclosure so that the internal device thermostat does not operate.

What to do?

1. Provides some sizeable vents above and below the heat sink.
2. Make sure the heat sink fins are vertical.
3. Buy a heatsink with the highest thermal conductivity - aim for 0.25C per Watt. See:

https://www.sensata.com/sites/defau...urproducts_HS-Series-Heat-Sinks_brochures.pdf

4. Incorporate a computer type cooling fan to force cooler outside air into the electrical cabinet and push out the warmer air inside the cabinet.
 
Last edited:
I suspect the problem is caused by the ssr becoming too hot and its internal thermostat acting to shut off the relay. I have a query with sensata/crydom to confirm as I suspect their latest next generation* D2425 SSRs contain an electronic thermostat to protect its electronics. Certainly the D2425 specification says the maximum ambient temperature is 80C, and at this temperature and above the current it can handle must be reduced ie the device de-rated from 25A. And the reference below describes an internal thermostat within the SSR package.

* The previous SSR was an earlier generation I reckon without a thermostat. Note the original SSR was assembled in Mexico whereas the new one does not mention where it was assembled.

https://www.sensata.com/sites/defau...tection-for-solid-state-relays_whitepaper.pdf

At the moment there are two problems with the way the SSR is installed. The first is the fins are horizontal - they should be vertical to maximise cooling by convection flow of air over the heat sink. The second it appears the SSR and heatsink is within a sealed enclosure adjacent to the very hot oven chamber. The SSR even with a heatsink properly orientated will have great difficulty keeping cool enough inside this enclosure so that the internal device thermostat does not operate.

What to do?

1. Provides some sizeable vents above and below the heat sink.
2. Make sure the heat sink fins are vertical.
3. Buy a heatsink with the highest thermal conductivity - aim for 0.25C per Watt. See:

https://www.sensata.com/sites/defau...urproducts_HS-Series-Heat-Sinks_brochures.pdf

4. Incorporate a computer type cooling fan to force cooler outside air into the electrical cabinet and push out the warmer air inside the cabinet.
After the oven has reached 300 degrees if I touch the SSR relay it is at room temperature, it is not hot, the heatsink instead is lukewarm. I think everything is ok, there is no overheating. Anyway, thank you all for the advice and help you are giving me.
 
any safety limit thermostat hiding in there anywhere?
it would probably be inline with one of the wires that go to the resistor.
 
Please take two photos showing the full details of the rear of the MC101 controller (view A) and of the specification plate (B).

Do you have a record of how you have programmed the MC101?

What is the component just above the MC101 with red coloured connectors?
 

Attachments

  • nuovo_relay_pannello_dx_LI.jpg
    986.2 KB · Views: 44
Has the new controller been properly set up? Many temperature controllers need to have a profile set to match the heating element & oven specs (sometimes known as PID tuning) which let the controller know how long that specific oven takes to heat up to various temperatures. Then if the oven deviates a lot from that known range, the controller will shut down as a safety precaution. That might be why on one occasion it stopped at 80+ degrees, but then went to 300+ degrees the next time (perhaps it had not cooled down inbetween?)
There might be a "PID" tune function in the controller

Tim
 
Please take two photos showing the full details of the rear of the MC101 controller (view A) and of the specification plate (B).

Do you have a record of how you have programmed the MC101?

What is the component just above the MC101 with red coloured connectors?
A strange thing has happened, now when I turn on the oven the red light mounted on the panel near the thermoregulator turns on and the heating starts too, but after about 30 seconds it turns off and the heating also stops working, that light indicates whether the oven is heating or not. The light must remain on throughout the heating process. For example, if the thermoregulator reaches the maximum temperature set, the light and heating switch off and switch on again only when the thermoregulator decides to start heating again to keep the temperature constant. I never paid any attention to whether or not the light came on even when I had problems with increasing the temperature, I would not want the problem to be the same.

Is it possible to start the heating by disconnecting two wires of the thermoregulator and connecting them together in order to exclude the thermoregulator and check if the problem depends on it or on something else? If so, which wires should I connect to each other? I am attaching a photo of the thermoregulator, the wires present are the number 1, 2, 3 and 4.

(The component above the red light is a timer, if the knob is turned and set for example to two hours the heating of the oven will be prevented for two hours, after two hours the heating would restart. To exclude the component I disconnected the wires by connecting them together, I came to the conclusion that it has nothing to do with the problem.)
 

Attachments

  • luce.jpg
    271.4 KB · Views: 27
  • foto25_.jpg
    121.1 KB · Views: 27
  • foto24_.jpg
    119.8 KB · Views: 28
Greetings from London.

Please post a picture of how the wires have been connected to the terminals on the back of the MC101 controller. The temp sensor uses the terminals I have circled. I am surprised you mentioned terminals 1, 2, 3 and 4 for the temp sensor because the temperature sensor is connected to 8, 9 and 10 dependent on whether it is resistive type or a thermoelectric type.

Please show me a picture of the temp sensor fitted at the moment including any markings. Do you have its details? Do you know whether it is temperature sensor using the change of its resistance (RTD type) to measure temperature or a thermocouple (TC type) which generates a voltage dependent on the temperature? This is important because the controller you have, the MC101-611, has (6) relay and SSR outputs and PID control, (1) upper limit alarm and only operates with a (1) thermocouple. Thus, there should only be connections to terminals 9 and 10 for the thermocouple input. Terminal 8 is not used.
 
If you have fitted a thermo couple it is important to connect its wires to match the polarity of terminals 9 (-) and 10 (+).
 
If you have fitted a thermo couple it is important to connect its wires to match the polarity of terminals 9 (-) and 10 (+).
Yes it is connected, I forgot to enter the numbering of the wires here in the forum, however it is connected with the number 9 and 10. The thermocouple are the green wire and the red one. The wires are connected with the right polarity.
 

Attachments

  • photo_2022-07-01_12-18-41.jpg
    116.7 KB · Views: 23
Looks like the ssr is connected to the relay output
it should be connected to the ssr output terminals.
however, it May not be as simple as moving them from one set of terminals to another.
you need to look at the instructions for the temperature controller to see the correct way to wire the ssr to the controller
 
Looks like the ssr is connected to the relay output
it should be connected to the ssr output terminals.
however, it May not be as simple as moving them from one set of terminals to another.
you need to look at the instructions for the temperature controller to see the correct way to wire the ssr to the controller
I based on how the previous Eliwell EWTQ905 thermoregulator was connected, the previous thermoregulator had an internal relay which drives an SSR, but the SSR cannot be connected directly to numbers 11 and 12 otherwise the oven does not work and the thermoregulator would go crazy. The oven is designed to be connected in this way.
 
The temperature controller is designed to drive the ssr direct from its ssr output.
I really think you are going to need someone who has the knowledge to come and fix this for you.
 
The D2425 requires a direct current control voltage signal. From where is this voltage signal currently obtained which is at the moment routed via the normally open no volt contacts in the controller to the ssr? The D in D2425 indicates direct current control whereas an A as in A2425 would mean alternating current control signal.
 
Last edited:
The D2425 requires a direct current control voltage signal. From where is this voltage signal currently obtained which is at the moment routed via the normally open no volt contacts in the controller to the ssr? The D in D2425 indicates direct current control whereas an A as in A2425 would mean alternating current control signal.
There is a Fagor B40 C5000 / 3300 rectifier bridge which has been replaced with a new one just to exclude it from the possible cause of the problem that does not make the oven work.
 

Attachments

  • fagor.jpg
    106.2 KB · Views: 18
if You are determined to use the relay output, have you reprogrammed the relay output to be heat instead of an alarm of some type?
 
The direct current wires come out of the respective polarities of the rectifier bridge and go straight into the input of the SSR relay.

Instead the alternating current wires of which I am attaching the photos are connected to several wires.

As for the alternating current instead (measuring with the tester at the output it says 228 v):

The white wire coming out of the SSR at the top taped together with a black wire goes to the resistance, the black wire instead goes to the panel light which turns on when the heating is in progress. The other wire that comes out of the light arrives in the blue connector present in the power supply of the thermoregulator, they are two wires in the same connector.

The blue wire that starts from the SSR relay ends up in the terminal block next to the rectifier bridge, it is taped together with another wire which goes into the first double connector on the power button at the top, the other part of the double connector goes to the timer and the other wire coming out of the timer goes into the first red power connector on the thermoregulator.

Instead, the last black wire on the right in the terminal board ends up in connector 4 of the thermoregulator.
 

Attachments

  • foto32.jpg
    97.6 KB · Views: 22
  • foto34.jpg
    133.5 KB · Views: 17
  • foto33.jpg
    67.3 KB · Views: 15
  • foto35.jpg
    348.2 KB · Views: 19
These are my latest thoughts on why your oven is not working. The D2425 is a 'zero crossing' device. It will only turn on when the mains cycle crosses the zero Volts axis. The condition for it turning is a trigger voltage greater than 3Vdc and a mains voltage less than the maximum allowable voltage for turn on at zero crossing. I show these in my attached diagram.

The trigger voltage is currently derived from the mains 240V cycle via a step down transformer to 24V ish (I cannot remember exact value). The stepped down 24 ac waveform is in synchronism with the mains cycle as I show in the diagram. Thus both the 240V ac waveform and the 24V waveform are in phase and cross over at 0V at the same times. The slope of the 240V ac waveform is greater than the slope of the 24 V ac waveform.

The 24V ac waveform is passed through a full wave rectifier to produce the green waveform . This is a unidirectional voltage but not constant, drops to zero volts and for a short period at crossover is not greater than the minimum 3V dc to trigger the D2425.

I think that the ssr is not triggering reliably. Sometimes the trigger voltage is greater than 3V dc before the mains cycle exceeds the maximum crossover start conduction voltage - the ssr turns on and powers the element.

But at other times (and maybe temperature dependent) the mains cycle exceeds the maximum crossover start conduction voltage before the trigger voltage exceeds 3V dc - so the ssr does not turn on.

The ssr requires a constant unidirectional voltage signal or at least a voltage which switches between 0V and greater than 3 V dc for reliably triggering into conduction. I attempt to show this bottom right.

What to do?

Place an electrolytic high temperature capacitor - say 1000 microFarads 63Vdc electrolytic - across the terminals 3 and 4 of the ssr - ensure polarity of capacitor. Or use the controller's dedicated ssr output which has a voltage waveform suited to signal the D2425 to start conduction at crossover because it instantly exceeds 3V ie: it does not follow the mains cycle waveform.

If you try the capacitor solution buy a few of these:

RS PRO 1000μF Electrolytic Capacitor 63V dc, Through Hole | RS Components - https://uk.rs-online.com/web/p/aluminium-capacitors/7076666
 

Attachments

  • E94770CC-1218-49D6-8F26-5B20A43B3FBB.jpeg
    239.9 KB · Views: 20
Last edited:
These are my latest thoughts on why your oven is not working. The D2425 is a 'zero crossing' device. It will only turn on when the mains cycle crosses the zero Volts axis. The condition for it turning is a trigger voltage greater than 3Vdc and a mains voltage less than the maximum allowable voltage for turn on at zero crossing. I show these in my attached diagram.

The trigger voltage is currently derived from the mains 240V cycle via a step down transformer to 24V ish (I cannot remember exact value). The stepped down 24 ac waveform is in synchronism with the mains cycle as I show in the diagram. Thus both the 240V ac waveform and the 24V waveform are in phase and cross over at 0V at the same times. The slope of the 240V ac waveform is greater than the slope of the 24 V ac waveform.

The 24V ac waveform is passed through a full wave rectifier to produce the green waveform . This is a unidirectional voltage but not constant, drops to zero volts and for a short period at crossover is not greater than the minimum 3V dc to trigger the D2425.

I think that the ssr is not triggering reliably. Sometimes the trigger voltage is greater than 3V dc before the mains cycle exceeds the maximum crossover start conduction voltage - the ssr turns on and powers the element.

But at other times (and maybe temperature dependent) the mains cycle exceeds the maximum crossover start conduction voltage before the trigger voltage exceeds 3V dc - so the ssr does not turn on.

The ssr requires a constant unidirectional voltage signal or at least a voltage which switches between 0V and greater than 3 V dc for reliably triggering into conduction. I attempt to show this bottom right.

What to do?

Place an electrolytic high temperature capacitor - say 1000 microFarads 63Vdc electrolytic - across the terminals 3 and 4 of the ssr - ensure polarity of capacitor. Or use the controller's dedicated ssr output which has a voltage waveform suited to signal the D2425 to start conduction at crossover because it instantly exceeds 3V ie: it does not follow the mains cycle waveform.

If you try the capacitor solution buy a few of these:
In the input of the relay and at the output of the rectifier bridge the measured direct current is 22.6 volts. When the heating process is on, the DC current measured at the SSR input is 22.3-22.4v instead when the heating process is off, it is approximately 22.6-22.8v.
 

Attachments

  • ssrinput.jpg
    345.1 KB · Views: 7

Reply to SSR relay problem solution in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock