I’ve got my P16th edition papers in 2006 so not a total beginner (I’m plumber as my trade tbh) but this pull chord bathroom light is not working and if trips the consumer unit .

Basically the old switch broke so I took a photo of the wiring before fitting a new light.

And it doesn’t work.

The brown an red wires are live and the two connect together are live too. I test them with this blue pen tester .

I’m gonna include photos of everything so any help be great thx
 
TL;DR
I know what I’m doing but basically I’ve no idea what to do here. I’ve just copied what was there before

Attachments

  • image.jpg
    image.jpg
    362.2 KB · Views: 39
  • 0A51F626-B8EB-43C0-A335-3A621B71B4C9.jpeg
    0A51F626-B8EB-43C0-A335-3A621B71B4C9.jpeg
    350.7 KB · Views: 33
  • 4130C53C-8A03-426D-8263-9CE4ACF0C088.jpeg
    4130C53C-8A03-426D-8263-9CE4ACF0C088.jpeg
    408.8 KB · Views: 31
  • IMG_7254.MOV
    IMG_7254.MOV
    4.6 MB
  • IMG_7255.MOV
    IMG_7255.MOV
    14.6 MB
  • 4718D26D-FFEC-473F-A58D-2F3949F94275.jpeg
    4718D26D-FFEC-473F-A58D-2F3949F94275.jpeg
    408.8 KB · Views: 32
  • 1A3B9300-6B5C-477B-ABED-6DAC4415246E.jpeg
    1A3B9300-6B5C-477B-ABED-6DAC4415246E.jpeg
    350.7 KB · Views: 35
  • 5F1F3656-4B2C-463A-BB7D-6379D6B21998.jpeg
    5F1F3656-4B2C-463A-BB7D-6379D6B21998.jpeg
    419.9 KB · Views: 35
  • image.jpg
    image.jpg
    690.5 KB · Views: 33
  • image.jpg
    image.jpg
    353.3 KB · Views: 27
What I would expect at the pull cord position is that the switch would have been between the red and brown wires, the two earth cores properly sleeved and connected to the switch earth terminal (if there is one), and the black and blue wires connected together by a wago or terminal block isolated from everything else.
Then at the light fitting, traditional connections of L, N and E.
Is this how you have tried wiring it?
Your old switch is two way, but it looks like only the two screws on the left side (third photo) have been used- I'm assuming there aren't enough wires for a two way circuit. Is there another switch for this circuit?

Tidying up of wire lengths and sleeving needed!

The above rather rashly assumes wire colours have been used for their traditional purposes.

Also be wary of quirks of pen tester.
 
Last edited:
What I would expect at the pull cord position is that the switch would have been between the red and brown wires, the two earth cores properly sleeved and connected to the switch earth terminal (if there is one), and the black and blue wires connected together by a wago or terminal block isolated from everything else.
Then at the light fitting, traditional connections of L, N and E.
Is this how you have tried wiring it?

Tidying up of wire lengths and sleeving needed!

The above rather rashly assumes wire colours have been used for their traditional purposes.

Be wary of quirks of pen tester.
Thanks for replying so fast but that’s what I did the red in common, brown L1, then the Earths to to E box (u can see where it’s been scorched)

I’ve got a traditional multi meter and so which wires would I test with Red and Black pls?

I thought the pen test was a bit crap when the Earth cable would beep the pen after a few secs!

Thsnks in. Advance (if u reply)….!
 
Thanks for replying so fast but that’s what I did the red in common, brown L1, then the Earths to to E box (u can see where it’s been scorched)

I’ve got a traditional multi meter and so which wires would I test with Red and Black pls?

I thought the pen test was a bit crap when the Earth cable would beep the pen after a few secs!

Thsnks in. Advance (if u reply)….!
In your movie the black wire looks nicked - did it get trapped somehow? That bit needs cutting off if you have enough cable length.
Firstly what trips in the consumer unit - MCB or RCD or what?

What are the wire colours at the light fitting? (black/red, or blue/brown) - I mean the wire coming out of the ceiling.
If the new fitting is up, with power off you could disconnect switch and check for any short circuit (between L-E or L-N etc)

Sounds like your earth core may not be connected, or with all this bare conductor about, has got trapped and connected to something it shouldn't!
 
Last edited:
In your movie the black wire looks nicked - did it get trapped somehow? That bit needs cutting off if you have enough cable length.
Firstly what trips in the consumer unit - MCB or RCD or what?

What are the wire colours at the light fitting? (black/red, or blue/brown) - I mean the wire coming out of the ceiling.
If the new fitting is up, with power off you could disconnect switch and check for any short circuit (between L-E or L-N etc)

Sounds like your earth core may not be connected, or with all this bare conductor about, has got trapped and connected to something it shouldn't!
I’ll take some more photos and post them now
 
more photos
The trip switch is first one on the left
 

Attachments

  • 754A5946-9652-4825-BCDA-43586D96EBDB.jpeg
    754A5946-9652-4825-BCDA-43586D96EBDB.jpeg
    335.2 KB · Views: 22
  • 1D5A36DA-B2E6-46AF-8FE1-A2BFA965317E.jpeg
    1D5A36DA-B2E6-46AF-8FE1-A2BFA965317E.jpeg
    348.3 KB · Views: 25
  • 810DD0F0-ECD1-4B3E-AFC5-302D81459905.jpeg
    810DD0F0-ECD1-4B3E-AFC5-302D81459905.jpeg
    227 KB · Views: 22
  • 3FDA34D8-9667-4184-811F-9967BAE6FE00.jpeg
    3FDA34D8-9667-4184-811F-9967BAE6FE00.jpeg
    372.5 KB · Views: 18
  • C10247E8-05C1-43DC-8E72-93C4A6A4CD4D.jpeg
    C10247E8-05C1-43DC-8E72-93C4A6A4CD4D.jpeg
    311.1 KB · Views: 19
  • B5AF8C51-D4BF-4FDB-B6A1-30F8A824BDDE.jpeg
    B5AF8C51-D4BF-4FDB-B6A1-30F8A824BDDE.jpeg
    388.2 KB · Views: 19
  • 03E319AF-B04F-45ED-9578-6F8AE1DAF593.jpeg
    03E319AF-B04F-45ED-9578-6F8AE1DAF593.jpeg
    372.5 KB · Views: 18
  • 49286AF6-E2A3-4BA8-84CB-84550E631299.jpeg
    49286AF6-E2A3-4BA8-84CB-84550E631299.jpeg
    311.1 KB · Views: 19
  • DBF5529B-FC85-4ABB-8B45-66C28E63AEC4.jpeg
    DBF5529B-FC85-4ABB-8B45-66C28E63AEC4.jpeg
    227 KB · Views: 18
  • 6F9CCFF6-0A7D-4FE5-BC0B-07DA78749D73.jpeg
    6F9CCFF6-0A7D-4FE5-BC0B-07DA78749D73.jpeg
    345.9 KB · Views: 19
  • 4784BC13-8DBF-48CB-AAA8-C25225F40637.jpeg
    4784BC13-8DBF-48CB-AAA8-C25225F40637.jpeg
    324.2 KB · Views: 27
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
 
Last edited:
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
I’ve pulled the wires down and cut little bit grey sheathing off.

The other pictures are the light fittings where the wires connect to the lights themselves.

Then a picture of the consumer unit

Hope this helps!
 
I’ve pulled the wires down and cut little bit grey sheathing off.

The other pictures are the light fittings where the wires connect to the lights themselves.

Then a picture of the consumer unit

Hope this helps!
Just to clarify - there are two light fittings as well as the switch?
Have you already rewired the ceiling rose shown in the last photo (I mean the photo with the close up of the metal bar), with the two red wires in it?
Presumably you have two red, two black, and two earth feeding that light?
 
Last edited:
  • Like
Reactions: Bgy333
Just to clarify - there are two light fittings as well as the switch?
Have you already rewired the ceiling rose shown in the last photo (I mean the photo with the close up of the metal bar), with the two red wires in it?
Presumably you have two red, two black, and two earth feeding that light?
That’s a yes to 2 light fixtures

1st one

2 black
2 red
2 earth

2nd one

1black
1ted
1 earth
 
That’s a yes to 2 light fixtures

1st one

2 black
2 red
2 earth

2nd one

1black
1ted
1 earth
What I would check first, with power off, is disconnect the red and black at the switch, and with no bulbs in the light fittings, use the multimeter on ohms range, check there is infinite resistance (ie open cicuit) between black and red. Not ideal, but at least would rule out a direct short in this section. Have you done any simple continuity checks to see if any miss connections?

I'm not clear if you have the new lights installed, or if wires are still hanging from the ceiling? Are new lights now in place, or are cables still disconnected?
 
Last edited:
Please could you explain the series of events that lead to the breaker tripping?
Did it trip when you first turned the power back on after wiring the lights,
or did you switch the power on, nothing happened, then you pulled the switch cord, and the breaker tripped?
If the second, the pull switch might now be welded permanently on!

Normally one would expect to test a circuit before applying power to it, though that doesn't seem to be the DIY way!
 
What I would check first, with power off, is disconnect the red and black at the switch, and with no bulbs in the light fittings, use the multimeter on ohms range, check there is infinite resistance (ie open cicuit) between black and red. Not ideal, but at least would rule out a direct short in this section. Have you done any simple continuity checks to see if any miss connections?

I'm not clear if you have the new lights installed, or if wires are still hanging from the ceiling? Are new lights now in place, or are cables still disconnected?
The lights were installed before (by me) and worked fine, it’s when the old switch was faulty and I’ve gone to install the new one I’ve had problems of it tripping out. I just took a photo of the old wiring and copied it to the new switch
 
The lights were installed before (by me) and worked fine, it’s when the old switch was faulty and I’ve gone to install the new one I’ve had problems of it tripping out. I just took a photo of the old wiring and copied it to the new switch
OK I understand better, thanks.
It seems obvious to concentrate on there being something wrong in or around the new switch.
The way you've described wiring it is how I would have done it!

Do the lights work all of the time, and the mcb trips only sometimes, or how does the tripping manifest itself?
 
OK I understand better, thanks.
It seems obvious to concentrate on there being something wrong in or around the new switch.
The way you've described wiring it is how I would have done it!

Do the lights work all of the time, and the mcb trips only sometimes, or how does the tripping manifest itself?
As it is now ( or was when wired as everyone including me assumed was the correct way) it would work for a bit then trip out, I’ve decorated since the dodgy switch started being dodgy and as a typical tradesmen the wife keeps reminding me every f’n year to sort it it and this year seems the year ! So basically recently the lights have been removed and wires hanging down ( it’s fine it’s adults only house!) and the string tied up . When some one not familiar with it would pull the cord it would trip and you have to pull again otherwise it would constantly trip.
 
Tbh it could possibly have been the wiring but I just assumed the switch was broken so replaced it but just coped with no bathroom light for about 4 years lol
 
As it is now ( or was when wired as everyone including me assumed was the correct way) it would work for a bit then trip out, I’ve decorated since the dodgy switch started being dodgy and as a typical tradesmen the wife keeps reminding me every f’n year to sort it it and this year seems the year ! So basically recently the lights have been removed and wires hanging down ( it’s fine it’s adults only house!) and the string tied up . When some one not familiar with it would pull the cord it would trip and you have to pull again otherwise it would constantly trip.
Well from everything you've said it seems there has been, and still is, a long standing fault, where if the switch was on, the MCB would trip. That implies somewhere between the light switch and the last light fitting, there is a problem with the wiring. The fact that an MCB trips and not the RCD (assuming the latter works - have you tried the test button recently?) implies to me a more serious problem.
I think either you should get a professional in with a multifunction tester to investigate, or as a minimum, replace the cables in the ceiling with new, all the way from the switch to the first light and then to the second light.
 
  • Like
Reactions: DPG
What was wrong with the old switch? Could it have been the fault making the old switch appear to be faulty when it actually isn't?
Sounds like you're right!
 
  • Like
Reactions: DPG
I’ve just got my multi meter in the wires in the loft the blue and brown is showing no reading and the read and black a tiny one I’ll include a pic and show the settings on my multi meter, obv the wires are all dangling so if I’m supposed to be connecting 2 lives I’m not. Cos ones not live and the other minimal
 

Attachments

  • image.jpg
    image.jpg
    492.1 KB · Views: 13
  • image.jpg
    image.jpg
    580.3 KB · Views: 16

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can anyone help with my bathroom light pull chord switch?
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
40

Advert

Thread statistics

Created
Bgy333,
Last reply from
Avo Mk8,
Replies
40
Views
5,725

Advert