mortgage retention advice for current installation upgrade | Page 3 | on ElectriciansForums

Discuss mortgage retention advice for current installation upgrade in the UK Electrical Forum area at ElectriciansForums.net

W

walkthenrun

Hi guys,
i need to carry some work out to get my house to pass its mortgage retention, i had a mate from napit come round and do a electrical installation inspection condition report, as one of the retention on my mortgage is due to the old electrical installation. at the moment there is a 15 way merlin gerin consumer unit. I have identified all the circuit apart from one 15A breaker. anyway i was hoping to change the current unit to rcbo's i think this is probably the best thing at the moment considering the size of the house so if anything does go rong i can localise the problem more easily. guys i have come for advice as i dont know which unit to buy? am i doing the right thing by going for rcbo's. i need something that will allow me have at least 13 different circuits. the only thing i have found upto now is a Wylex 11 way Consumer Unit Type NH1104 that i could put 11 circuits on. The immediate advice my friend give me was to condition report was to update the consumer unit so that the shower is rcd protected, the lights in the bathroom are ip65. the supply to the summer house and the pond shed is in swa cable. is it possible to just take the current consumer unit and swap it directly for an 11 way rcbo consumer unit. would everything carry on working as it is working perfectly now.
i have identified each circuit as follows
1. annexe consumer unit and outdoor floodlight consumer unit (60A) (10mm cable and 2.5mm)
2. cooker (50A) (6mm)
3. upstairs sockets (32A) with two fuse spurs in garage from ring final in above main bedroom (2.5mm)
4. downstairs sockets (32A) (2.5mm)
5. 15A?
6. 5A lights in boiler room (G), garage(G), utility(G),main bathroom(U), small blue room(U), hallway(U), pink room(U) and kids room(U) G-ground U-upstairs (1.5)
7. shower (50A) (6mm 8.5kw shower clipped direct to wall)
8. main bedroom (U) and ensuite lights (U) (5A) (1.5mm)
9. kitchen(G) dining room(G) sitting room (G) and toy room lights (G) (5A) (1.5mm)
10. boiler (5A) (1mm)
11. Pond shed hager consumer unit (60A) (10mm)
12. summer house volex consumer unit (60A) (10mm)

some pictures are included thanks
[ElectriciansForums.net] mortgage retention advice for current installation upgrade
main consumer unit
[ElectriciansForums.net] mortgage retention advice for current installation upgrade
main c.u and outdoor lighting c.u
[ElectriciansForums.net] mortgage retention advice for current installation upgrade
pond c.u
[ElectriciansForums.net] mortgage retention advice for current installation upgrade
summer house c.u
[ElectriciansForums.net] mortgage retention advice for current installation upgrade
annexe c.u

thanks in advance for your immediate advice if any more pictures are required please let me know thanks
 
Last edited by a moderator:
So why are you trying to fit a 50A or higher MCB/RCBO?
a 45A would be adequate for now but i would in the future like to upgrade the shower to a 10.5kw but if i was going to upgrade the lot now i would put a 10mm cable in and change the pull down d.p to a wall mounted one and also get the correct breaker from the initial installation
 
So why are you trying to fit a 50A or higher MCB/RCBO?
6mm 47A clipped direct and then voltage drop wouldnt have an advers affect over that distance, so a 45A c.b would be acceptable
8500/230=36.96A so 37A maximum current flowing
on 10.5kw/230=45.65A
10mm cable clipped direct 2c0re 63A 3core is 57A
 
Last edited by a moderator:
I dont mean this in a sarcastic way, but what is the fascination with people wanting to get a bigger and bigger showers. What is wrong with a 8.5kw?
 
I dont mean this in a sarcastic way, but what is the fascination with people wanting to get a bigger and bigger showers. What is wrong with a 8.5kw?

Why anyone would ever need a 10.5KW shower, i will never know!! I'm using a 4.2KW shower over here and it's more than just adequate for a good hot shower!!
 
Why anyone would ever need a 10.5KW shower, i will never know!! I'm using a 4.2KW shower over here and it's more than just adequate for a good hot shower!!

Maybe they want to re-enact a scene from Rambo, when he is in the police station...
 
Bet they don't sell many 10.5KW showers in France, where it seems the average domestic supply is limited to 12KVA!! ...lol!! ....It's only the daft British that want to be one better than the Jones next door!!! lol!!
 
OP: Id be more concerned about the 2.5mm cable going to MCB 1 (60A) for the outside lights than the shower cable.
 
OP: Id be more concerned about the 2.5mm cable going to MCB 1 (60A) for the outside lights than the shower cable.
i know this should be on its own 6A breaker cant see the floodlights drawing 60A if they are 160W thats pretty easy fix could easily go into lighting circuit with main bedroom as not in use at moment anyway and also wont probably have a large load when in use
 
I think you need to stop, look hard and plan before you do anything.

And get your "mate" involved, if he exists, because if he does, he and not us is the best person to advise you.

you know what the sad thing about this forum is... you come on for help, because you are unsure and you are learning and you want others opinions, i have got two mates who have offered one is napit and the other is niceic, it would have been good to have got other opinions of well qualified experienced individuals who dont have there head up there own a**. think about when you started you didnt know everything, you were helped along and you were thrown in the deep end, its a shame that people encourage one another with unsupportive and horrible comments like this. if you dont want to input please move on and let the people who do have a passion for what they do, have there input
 
you know what the sad thing about this forum is... you come on for help because you unsure you learning and you want guidance, i have got two mates who have offered one is napit and the other is niceic, it would have been good to have got other opinions of well qualified experienced individuals who didnt have there head up there own a**. you know think about when you started you didnt know everything you were helped along and you were thrown in the deep end, its a shame that people encourage one another with unsupportive and horrible comments like this. if you dont want to input please move on and let the people who do have a passion for what they do enjoy helping others.

think you have had a lot of helpful comments here. still waiting for you to let us know if there were any C1s or C2s on your napit mate's EICR. murdoch's post reflects this. if you have an EICR, then why not let us know the outcome?
 
think you have had a lot of helpful comments here. still waiting for you to let us know if there were any C1s or C2s on your napit mate's EICR. murdoch's post reflects this. if you have an EICR, then why not let us know the outcome?

as soon as i have a copy of the report il photograph it and put it up, should be tomorrow was not given it at the time as was told that if i didnt make the changes it would be down on the report as recommendations and hence would not pass and achieve certification to show as being safe and upto current standards, was also advised that sockets needed to be on rcd. was told to make changes, including a new consumer unit and then have the report completed. so when i was asked that is there are any c1 or c2 i phoned my mate anthony who told me installing the rcd would be a c3 and updating the consumer unit and installing the ip65 lights would also be c3. il have to wait and see now
 
the lack of RCDs is only a code C3 unless outdoors, as a C3 that means improvement recommended, a bit like an advise on your MOT. does not mean that the installation is unfit for continued use.
 
you know what the sad thing about this forum is... you come on for help, because you are unsure and you are learning and you want others opinions, i have got two mates who have offered one is napit and the other is niceic, it would have been good to have got other opinions of well qualified experienced individuals who dont have there head up there own a**. think about when you started you didnt know everything, you were helped along and you were thrown in the deep end, its a shame that people encourage one another with unsupportive and horrible comments like this. if you dont want to input please move on and let the people who do have a passion for what they do, have there input

Yup, and I've got a mate who's got 25 years more than me and I still use him, and he uses me for advice - and where necessary we visit each others "jobs" so we can actually look at the jobs first hand.
 
you know what the sad thing about this forum is... you come on for help.........................sion for what they do, have there input

Get a 'Satisfactory' EICR (ie no C1s or C2s) off your two mates, give it to your mortgage provider, get your £20K off their grubby little hands, then work on your installation at your leisure!!!
It's your own house and you're a Trainee Electrician, aware of any risks, go for it!
 
as for inline fans.....................
crack on mate, so long as you get a large air change rate they work wonderful, dont get wickes own inline as thats just about 45l/m whereas you can splash out and get a full on 140/160 l/m fan that will suck the water straight out the shower and out thru the fan before it even touches you lol.

people do tend to get pedantic on this site, but you have had some good advice, when you get your eicr, look thru it do the required work and for now ignore any C3's, get your dosh from el banko.
encourage your mates to show you or help you to understand where the faults are at the moment.
people on here can only speculate as to the best way forward, but your mates can give you proper informed advice
 
the lack of RCDs is only a code C3 unless outdoors, as a C3 that means improvement recommended, a bit like an advise on your MOT. does not mean that the installation is unfit for continued use.

thanks, i have spoken to my mate and he is saying the shower not being on rcd and the sockets not being on rcd are definately c3. advice is obviously appreciated, thanks your right it does not make it unfit for continued use
 
Yup, and I've got a mate who's got 25 years more than me and I still use him, and he uses me for advice - and where necessary we visit each others "jobs" so we can actually look at the jobs first hand.

i will be asking my mates for help and they will be helping me, with whatever work is carried out, but i do appreciate they have there own work and commitments too hence why i am trying to get all the help i can with this
 

Reply to mortgage retention advice for current installation upgrade in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
539
  • Question
It’s a much easier job to move it now with the build work if you don’t you’ll no doubt only end up with some electrician kicking up a stink...
Replies
22
Views
5K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
  • Question
The garden supply will have a 7kw sauna at a later date which has the 16mm swa 3 core to it
Replies
4
Views
1K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks